Old Substation in Five Years? Really?

Technology development has gone mad. Everything is automated, what’s needed and what’s not needed, and that’s definitely not good. Substation equipment, especially secondary systems, becomes obsolete and hard to maintain in a very short time. The main question is how to approach substation design, how much new technology to implement, and how it will be maintained after 5 years.

Top Issues that Seriously Worry Substation Designers
Top Issues that Seriously Worry Substation Designers

Power substations must be carefully designed, constructed, and operated to fulfill customer requirements at the minimal cost consistent with the required level of service. The conventional system may comprise substations for voltage transformation, sectionalizing, distribution, and metering many times between generation and utilization, so there are thousands of tiny important details.

When designing power substations, engineers MUST think about the future, both now and in the far future. In order to provide clients with sufficient service and ensure the physical and financial integrity of electrical systems, it is crucial to make plans in a timely manner.

Detailed in the long-term plan are the needs of a substation for both its immediate and distant future use. When you’re planning the first layout, keep the end goals in mind. Find out what provisions are required for ease of addition by comparing economic factors.

Before building begins, make sure that the development plans incorporate the philosophies of operating and protecting the systems and equipment. Engineers responsible for designing, operating, and maintaining the proposed equipment should assess any shifts in the utility’s conventional design principles. System functionality could be compromised by deviating from conventional designs.

In order to provide clear objectives and specifications for the substation’s design, an extensive analysis of fundamental characteristics must precede the detailed design phase.

Further factors to think about include circuit quantities, configurations, and ratings; protective relay schemes for systems and equipment; the need for specific equipment features related to surge protection; and necessary measures to prevent direct stroke.

Table of Contents:

  1. How System Impacts the Substation Design?
    1. Primary Power Plant
    2. Secondary Systems
  2. The Impact on the Substation Single-line Diagram
    1. Substation Configuration
  3. Impact on the Substation Bay
    1. Physical Environment
    2. Impact on Substation Equipment
      1. Primary Equipment
      2. Challenges in Upgrading Substation Automation
      3. Auxiliary Equipment
    3. Substation Operations
    4. Conclusions
  4. Attachment (PDF) 🔗 Download ‘Case Study on the Power Substation Design’

1. How System Impacts the Substation Design?

Let’s draws out some general observations and conclusions on the substation design at system, single line and bay level.

When we examine the impact of the various influences on substation design, there are a number of issues which are common to many of the scenarios. This technical article considers these various impacts.


1.1 Primary Power Plant

The substation infrastructure is most likely to experience increased power transfers to meet future demands. Greater interconnection of remote generation will require utilities to increase capacity using either series compensation, HVDC or real time monitoring to enhance ratings.

Inevitably, as equipment is pushed harder the electromagnetic stress seen by primary equipment will increase, utilities will need to be able to assess this risk.

The network topologies will need to be much more flexible to meet changing needs, this will see either network expansion or wider application of FACTS devices, the challenge will be coordinating these devices as more appear and possibly interact.

Adverse weather will directly impact on network security and the substation flexibility will determine the system resilience to these effects.

Figure 1 – Diagram of the large power plant

Power plant, larger units
Figure 1 – Diagram of the large power plant

Go back to Content Table ↑


1.2 Secondary Systems

The application of Wide area monitoring, control and protection will become more prevalent as System Operators are faced with more dynamic networks and large scale interconnections. Embedded generation and active control within distribution networks will require significant coordination between neighbours and make traditionally separate networks much more interdependent on each other.

The communication necessary to support these developments will be central to the security and reliability of the strategy. There is likely to be a greater dependency on these systems to facilitate the changes in power networks.

Compared with the substation primary plants and instrument transformers which generally remain in-service for long life-cycles, renewed only when physically or mechanically life-expired, the secondary systems (protection and control equipment) are often changed more frequently.

The short life of protection and control equipment means that during the typical 40 year asset life of primary switchgear the secondary equipment needs to be replaced at least once and probably twice.

Based on the statistics from the construction industry, currently achievable replacement rate for protection and control systems is about 3-5% per annual. It would take around 20+ years or less to complete a whole cycle of a replacement. However, the modern protection and control equipment asset life is 15 years, and in many cases, they only last 10 years due to the availability of technical support and technology change.

In addition, the replacement and maintenance of substation secondary equipment may also lead to downtime, which negatively influences the overall availability of the substation. One factor which contributes to this problem is the complex wiring required for the installation of a relay. Another possible contributing factor is relay obsolescence. If a new relay has to be installed, it may require a new configuration in order to communicate with the existing substation equipment, and this may not be possible without the use of expensive protocol converters.

Normally, outages for replacement of protection and control devices are eight weeks in duration and National Grid would like to reduce these to typically one to two weeks.

Figure 2 – Secondary equipment: Control and protection panel

Secondary equipment: Control and protection panel
Figure 2 – Secondary equipment: Control and protection panel (photo credit: Nonofo Unami Ketlhaotswe via Linkedin)

One way to overcome the problem is to develop a new architecture for substation secondary systems by deploying some new technologies such as standard interface modules, process bus and IEC61850 communication protocol. The deployment of IEC61850 process bus technology will allow ongoing substation secondary equipment retrofitting (refurbishment) projects to proceed whilst limiting the duration and frequency of circuit outages, required to facilitate the work.

Once the new technology is installed, secondary equipment renewals occurring mid-life in the primary plant lifecycle can be undertaken in a safer, quicker and easier way with much reduced outages of primary systems.

This will also enable vendor interoperability and easier modification and extension of the secondary schemes, particularly allowing reconfiguration and feature enhancement by software means, rather than the modification of wiring as would have been the case in the past.

As the new secondary systems transmit data of CT and VT analogue signals via the process bus, this poses no safety risks of opening CT circuits, and hence improving the safety when the protection replacement is carried out with primary circuit in service.

Interesting Study – Applying directional overcurrent relays in ground fault protection of transmission lines

Applying directional overcurrent relays in ground fault protection of transmission lines

Go back to Content Table ↑


2. The Impact on the Substation-single Line Diagram

If we look at the effect upon the single line diagram (SLD) of the substation then one of the immediate effects may be the short circuit rating required for the plant within the substation. Depending upon the device being connected this may require an increase in short circuit level or in some cases (fault current limiters) may enable simplification of the SLD by allowing greater bussing of equipment without too many sections.

The increase in harmonics on the network may give rise to a greater need for filters, either passive or active, however most transmission applications should be specified to reduce or, at least, not worsen system harmonics.

New technologies and integrated applications will affect the substation configuration and insulation coordination dynamics. Application of surge arresters and controlled switching will need to be considered to maintain adequate safety margins.

This is particularly important for electronic components, which have a very low tolerance to overvoltages.

Figure 3 – Single-line diagram

Single-line diagram
Figure 3 – Single-line diagram

Go back to Content Table ↑


2.1 Substation Configuration

The reliability and maintenance impact of new switchgear should encourage utilities to examine new running arrangements. Much longer intervals between corrective maintenance could lead to different strategies such as replace and maintain off line, rather than in situ maintenance.

For substations incorporating new technologies consideration needs to be given to the operation and running arrangement when the device has to be disconnected for maintenance or under fault conditions.

Reducing the duration of outage or bypass arrangements may be required and care needs to be taken with the protection arrangements to cover both conditions.

The utility will need to consider the relative cost of getting outages in the future against spare switchgear, so that rapid replacement and offline maintenance can be employed. Any element of wide area protection will also need to coordinate with these changes.

As Substation Life cycle costing becomes a more accepted method for design selection then different single line diagrams may be considered.

Further Study – Guidelines for HV substation designers to properly analyze, size and select equipment

Guidelines for HV substation designers to properly analyze, size and select equipment

Go back to Content Table ↑


3. Impact on the Substation Bay

Whatever new functionality is employed to affect system level attributes such as fault level, power flow, etc., it is invariably going to have a significant impact at the bay level.


3.1 Physical Environment

Once the substation configuration is defined, detailed design can take place to specify aspects of the substation and equipment. Space is an obvious limitation in most substations where new equipment needs to be installed. The space requirements need to consider the connectivity required with other plant items, the required electrical clearances, clearance required for electromagnetic effects, access for initial installation and maintenance.

The impact on civil works may include oil containment and fire requirements if the new devices introduce oil immersed transformers and if air cored reactors are present care has to be taken with the reinforcing bar arrangements, structures and earthing to avoid heating from closed loops.

Natural cyclical climate change is going to have an increasingly direct impact on switchgear specifications such as operational temperature ranges and on the physical location of equipment (e.g. mechanism boxes).

Substation marshalling must be designed to ensure immunity to interference generated from any new applications installed in the substation which may induce transients into site cabling. Use if optical fibre will help to alleviate this problem special care is needed in the design of the earthing system, to ensure safety whilst avoiding interference into control circuits and avoiding large circulating currents from flowing due to electromagnetic induction.

Figure 4 – Marshalling box of current transformers

Marshalling box of current transformers
Figure 4 – Marshalling box of current transformers

Audible noise can have a significant effect on the equipment specification and subsequent testing. At the design stage the various options should be investigated such as indoor build, location or operational modes before writing very onerous equipment specifications.

A directive on EMC regarding substations as fixed installations will require the designer to consider any effects more critically since the substation is now seen a source and will need to demonstrate compliance with the standards.

Interesting Reading – Why We Still Ignore Intentional Destructive Electromagnetic Threats to Power Systems

Why We Still Ignore Intentional Destructive Electromagnetic Threats to Power Systems

Go back to Content Table ↑


3.2 Impact on Substation Equipment

There is a move towards modularity and design standardisation in an effort to reduce costs. This does mean utility specific adaptations are more difficult to make and traditional utility procedures may require review.


3.2.1 Primary Equipment

On going SF6 gas containment and tightness is a major concern among utilities, lifecycle factors need to be addressed at the specification and installation stage to ensure the desired objective of zero leakage can be reasonable achieved. Any new switchgear, especially at transmission will require SF6 gas handling, this will require training and certification under new EU regulations.

Utilities will need to specify current transformers and voltage transformers with a view to meeting future digital protection and control needs.

Worth Studying – Voltage and current measurement in modern digital high voltage substations

Voltage and current measurement in modern digital high voltage substations

Go back to Content Table ↑


3.2.2 Challenges in Upgrading Substation Automation

Substation automation will experience the greater change as interfacing new to old legacy wiring, the transfer to powered relays and isolation from the instrument transformer secondary (high impedance). There will also be a high degree of technology obsolescence.

Secondary asset replacement occurs more frequently and switchgear interfacing is proving to one of the most complex challenges. The fact that the secondary wiring may need to be changed a couple of times during the life of switchgear results in long outages to facilitate the replacement.

IEC 62271-3 aims to address some of the issues facing primary and secondary integration. Therefore in order to facilitate faster secondary asset replacement additional costs may need to be incurred at the primary asset investment stage.

Figure 5 – Digital protection panel: IEC 61850 communications

Digital protection panel: IEC 61850 communications
Figure 5 – Digital protection panel: IEC 61850 communications

The implementation of IEC 61850 is underway and utilities need to develop their application requirements and the associated interfaces to any system management tools.

As utilities move from copper multi-core to fibre based marshalling systems, this forces the utility to establish standard termination and data protocols. Utilities need to develop their own IEC 61850 configuration requirements. New tools and training will be necessary to configure multifunctional protection ‘black boxes’ safely and reliably.

Substation and network communication is a major issue. Before many of the new initiatives can be considered rules about ensuring secure portals, management of firmware changes, software version control and access must be resolved. Ensuring that utility personnel can interrogate and download fault recorders or setting is necessary, while at the same time preventing unauthorised access.

As more functionality is incorporated into equipment or Wide area systems are developed, the testing according to existing standards may require some interpretation and development, both in the factory acceptance tests and more importantly at final commissioning.

Upgrade Example – Behind upgrading the 50+ years old 132/11 kV substation

Behind upgrading the 50+ years old 132/11 kV substation

Go back to Content Table ↑


3.2.3 Auxiliary Equipment

Most of the new functionality will increase the pressure on auxiliary systems. The steady state loading is increasing and dependency on the DC supply is becoming more important than ever.

Additional AC supplies will be required for cooling of components, additional DC supplies for the control and protection. The protection design needs to consider the particular requirements of the new types of device and also the impact these devices may have upon the performance of existing system protections such as distance relays.

Interlocking may be required for both operational and safety reasons.

Further Study – Auxiliary DC power system used for fault detection, trip coils and remote operation

Auxiliary DC power system used for fault detection, trip coils and remote operation

Go back to Content Table ↑


3.3 Substation Operations

One of the common requirements for most of these new functionalities is that existing maintenance strategies may need to be reviewed. In many cases this may require procedural changes, however in a number of cases specific strategies will be required. This may result in training for substation staff or alternatively service agreements with the supplier. In both cases the costs can be large whether it is in terms of contracts or substation resource tied up in training.

Where diagnostic tools are employed such as condition monitoring or analysis provision for maintenance or calibration of these services will need to be made (exchanging one maintenance intensive system for another), albeit the latter does not tend to incur outages.

New skill sets will be required by substation staff, particularly in the field of information systems and possibly software programming. Staff will need to be IT literate, to interrogate secondary systems, implement test procedures and perform diagnostics on substation automation.

The manner in which condition monitoring is employed will enable the utility to optimise its maintenance and asset replacement strategies. The utility will need to concentrate on how the information is used within the organisation to maximise any benefit, liberal application of condition monitoring without a good input into the maintenance and asset management decision making tools will be ineffective.

Important Reading – Substation Safety and Switching Rules You MUST Follow

Substation Safety and Switching Rules You MUST Follow

Go back to Content Table ↑


4. Conclusions

Engineers employed in substation design must adopt different strategies to manage change on the system, the article has only mentioned technology biased solutions, not operational or commercial alternatives. However, business and commercial processes will impact on the choice of solution employed. Conversely, behind commercial solutions there might be a need for better technical definitions concerning equipment interfaces, removable containers, post delivery support etc.

The transmission and distribution industry is by its very role conservative, which is reflected in the vintage of installed equipment and the adoption of traditional technologies and architecture.

In many cases this is a good thing, but as the world changes utilising developments in other industries and technology transfer is necessary to remain functional and competitive.

Some of the key issues which can be drawn from the work are:


Key Issue #1

In most cases some form of Life-Cycle Costing is required to identify the optimal solution for the utility. Depending on the value utilities place on key issues such as operation and maintenance, this will affect the suitability of different solutions.

Good Reading – The life of a power substation project: Design, construction, erection and commissioning

The life of a power substation project: Design, construction, erection and commissioning


Key Issue #2

Substation designers need to consider recommendations on the application of technology and not just the technical specification. This will help to ensure the desired conclusion is reached without project delay or exceeding the budget.


Key Issue #3

There is a trend towards modularity and more standardisation of solutions, which must be considered when reviewing maintenance, refurbishment and substation extension plans.


Key Issue #4

The emphasis on maintenance is changing from intrusive testing to diagnostics and monitoring. This is moving the volume of work from the substation to the office. This strategy however requires the monitoring equipment to be more reliable than the switchgear.

Unfortunately this is not the case, so a lot of time is spent investigating the monitoring system.


Key Issue #5

New resource and skill sets are necessary (software programming and telecoms) to enable the End users to maximise the benefit from modern technology. However this must be combined with experience from the past.

Good reading – Technical Documentation for a Turnkey Substation

Technical Documentation for a Turnkey Substation


Key Issue #6

Detailed and bespoke engineering is necessary when interfacing between different vintages of equipment. This will impact on resource, system access and commissioning programmes.


Key Issue #7

Substation automation is very much concerned now with managing technology obsolescence and software version control. The scope of the protection engineer is broadening.

Suggested Course – The Power Substation Fundamentals Course: Theory, Equipment, Earthing, and Design

The Power Substation Fundamentals Course: Theory, Equipment, Earthing, and Design
The Power Substation Fundamentals Course: Theory, Equipment, Earthing, and Design

Go back to Content Table ↑


5. Attachment (PDF): Case Study on the Power Substation Design

Download: Case Study on the Power Substation Design (for premium members only):

Membership Upgrade Required

This content is not available in your premium membership plan. Please upgrade your plan in order to access this content. You can choose an annually based Basic, Pro, or Enterprise membership plan. Subscribe and enjoy studying specialized technical articles, online video courses, electrical engineering guides, and papers.
With EEP's premium membership, you get additional essence that enhances your knowledge and experience in low- medium- and high-voltage engineering fields.
Good to know: - Save 50% on all video courses with Enterprise plan.
Upgrade
Already a member? Log in here

Go back to Content Table ↑

References:

  1. The impact of new functionalities on substation design by Working Group B3.01

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Edvard Csanyi - Author at EEP-Electrical Engineering Portal

Edvard Csanyi

Hi, I'm an electrical engineer, programmer and founder of EEP - Electrical Engineering Portal. I worked twelve years at Schneider Electric in the position of technical support for low- and medium-voltage projects and the design of busbar trunking systems.

I'm highly specialized in the design of LV/MV switchgear and low-voltage, high-power busbar trunking (<6300A) in substations, commercial buildings and industry facilities. I'm also a professional in AutoCAD programming.

Profile: Edvard Csanyi

2 Comments


  1. Asif
    Oct 02, 2025

    Established new 33/11 kv sub station


  2. SAOLOAN NAIBORHU
    Sep 29, 2025

    Thank you very much for send to my Email some useful articles in web “Electrical Engineering-Portal.com” for your details explanation about Design of Substation.

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.
Whitepaper: How to Improve Risk Decisions for Power Systems - Prioritizing vulnerabilities with full operational context