Transformer insulation structure
This routine test aims to measure the partial discharges which may occur in the transformer insulation structure during test. Partial-discharges are electrical arks which form the surges between electrodes of any area of the insulating media of a transformer between the conductors.
Transformer routine test - Partial discharge measurement
Transformer routine test – Partial discharge measurement (photo credit: wtc.com.au)
These discharges may occur in air bubbles left in the insulating media, gaps in the solid materials or at the surfaces of two different insulators. Although these discharges have small (weak) energy, the thermal energies due to these discharges can cause aging, deformation and tear of the insulating material.
The following conditions can be determined during partial-discharge measurement:
  1. To determine whether a partial-discharge above a certain value has occurred in the transformer at a pre-defined voltage.
  2. To define the voltage values where the partial-discharge starts by increasing the applied voltage (partial-discharge start voltage) and the value where the partial-discharge ceases by decreasing the applied voltage (partial-discharge cease voltage).
  3. To define the partial-discharge strength at a pre-defined voltage.
How Partial-Discharge occurs and measured magnitudes?
The structure where a partial-discharge occurred in an insulating media is shown in the simplified Figure 1. As seen on the simpliified diagram, the impulses forming on the discharge point cause a ΔU voltage drop at the transformer line terminals. This forms a measurable “q” load at the measuring impedance.
This load is called apparent load and given in pC (Pico-Coulomb) units.
During measurements: ΔU voltage drop, average value of apparent partial-discharge current, partial- discharge power, impulse count within a time unit, partial-discharge start and cease voltages can also be determined.
a) simple schematics of an insulator with gas gap b) equivalent circuit
Figure 1 – a) simple schematics of an insulator with gas gap b) equivalent circuit
Measuring circuit and application
Partial-discharge measurement structure of a transformer and related circuit in accordance with IEC 60270 is explained below.
Partial discharge measuring connection circuit
Figure 2 – Partial discharge measuring connection circuit
1. Supply generator
2. Supply transformer
3. Test transformer
4. Voltage transformer and measuring circuit
5. Filter
6. Measuring impedance
7. Selective switch
8. Measuring instrument and ossiloscope
qo – calibration generator
The measurement circuit in Figure 2 is formed according to Bushing-tap method stated in standards.
Before starting to measure, complete measurement circuit should be calibrated.
For this, a calibrator (Calibration generator) is necessary. The calibrator produces a q0 load with a predefined value. Calibrator is connected to the test material in parallel. The q0 load produced in the calibrator is read at the measuring instrument. These steps are repeated at all terminals of the transformer to be measured at no-voltage.
K = q0 / q0m
K – correction factor
q0 – load at the calibrator
q0m – load read at the measuring instrument
Application of the test
After the calibration operations are completed, the calibration generator is taken away from the measuring circuit. When the power system is connected (supply generator switch is closed), the voltage level will be too low (remenance level).
This value which is considered as the base noise (interference) level of the measuring system should be less than half of the guaranteed partial- discharge level.
Voltage level
The voltage is substantially increased up to the level stated by the specifications and in the meantime the partial-discharge values at the predefined voltage levels are measured at each measuring terminal and recorded. The voltage application period, level and measuring intervals are given in the induced voltage test section.
After the transformer is energised for measuring operations, the partial-discharge value read at the measuring instrument is multiplied with the predefined K correction factor, and real apparent partial-discharge value for each terminal is found.
q = K · qm
  • qm – load read at the measuring instrument m
  • K – correction factor
  • q – Real apparent load
Evaluation
The test is considered to be succesful if the partial-discharge value measured at the transformer’s measuring terminals is lower than predefined values or values stated in the standards and no increasing tendency is observed during test.
In addition to the measured partial-discharge level, the below conditions should also be considered in transformers:
  • Partial-discharge start and cease voltages are above the operating voltage.
  • Depending on the test period, partial-discharge level stays approximately stable.
  • Increasing the test voltage causes almost no partial-discharge level change.
Reference: Transformer Tests – BEST Transformers
10 Comments
  1. Jeff Seyfert
    Jun 14, 2022
    This is valuable website. Thank you for your explanations and insight.
  2. Sanjeev Sharma
    Oct 26, 2021
    Excellent knowledge sharing
  3. Hadi Salih
    Dec 04, 2018
    I am really appreciated for your valuable information in this portal.
  4. Maurice Anosike
    Mar 30, 2017
    You are really helping in spreading painstakingly researched knowledge to many of us. You are doing a great service to humanity. Once again, we appreciate you.
  5. nyasha nyakudya
    Apr 23, 2016
    Can someone tell me what is the acceptable range of partial discharges with which a power transformer can operate? generally
  6. PHUONG
    Apr 03, 2015
    Thanks alot ! You have experience analyse parttern Partial Discharge for Transformer, Cable, GIS..?
  7. wesonga michael
    Dec 24, 2014
    Gladly look forward to your innovation of such a learning forum!!
  8. Abdullah Habib Zia
    Dec 20, 2014
    Thanks a lot.
  9. rene lloren jr
    Dec 18, 2014
    hello!
    a great day for great minds!
    regards,
  10. Durga prasad
    Dec 15, 2014
    Really ur great sir because of ur sharing or knowledge to all thats why ur great sir all the best sir
Leave a Reply to Maurice Anosike
thirty seven  −    =  35
ETAP technical webinars