Home / Technical Articles / What Is a Good Ground Resistance Value?
Zero Ohms… Not Really!
The goal in ground resistance is to achieve the lowest ground resistance value possible, that makes sense economically and physically, when contacting the earth, also known as the soil/ground rod interface.
Ideally, a ground should be zero ohms of resistance, but…
Unfortunately, there is not one standard ground resistance threshold recognized by all certifying agencies.
The NFPA and IEEE recommend a ground resistance value of 5 ohms or less while the NEC has stated to “Make sure that system impedance to ground is less than 5 ohms specified in NEC 50.56. In facilities with sensitive equipment it should be 5ohms or less.
Copper Earth Rod thermoweld connection at a 33kV Substation in Nakheel, UAE
Copper Earth Rod thermoweld connection at a 33kV Substation in Nakheel, UAE (photo by Muhammad Adnan; Substation Designer via Flickr)
The telecommunications industry has often used 5 ohms or less as their value for grounding and bonding while electric utilities construct their ground systems so that the resistance at a large station will be no more than a few tenths of one ohm.
In general, the lower the ground resistance, the safer the system is considered to be.
Reference: Fluke Earth Ground Testing Fact – Distributor Training Program
87 Comments
  1. Jan Bailey
    Jan 25, 2023
    SANS10142-1 WIRING REGULATIONS CONTAINS THE PRINCIPLES TO BE FOLLOWED FOR THE WIRING OF PREMISES.
  2. PowerTrain
    Nov 12, 2022
    No one reads the questions so why ask
  3. Grace
    Nov 03, 2022
    What is earth fault ?
  4. delightsome
    Jul 19, 2022
    i got a reading of 5.81 ohms on a changeover switch gear earth point while the generator (350KVA) earth point gave a reading of 1,89 ohmns, is it safe?
  5. Bartolomeu Matina Kuese
    Jan 12, 2022
    Dear Sir,
    My enquiry is what is the value expected amp/ohm on Ground Pipeline ?
    I just performed a Ground Protection between Pipeline & offshore structure what tie in to the Sea Bed Anode ground is Cadweld on Pipeline which is coming from Offshore 30 inch Pipeline going onshore due to allow welding activities while the Pipeline is in-service liquids onto is Crude.
    ([email protected])
    Question what is the amp value ?
  6. Tarek Aboukhadra
    Aug 14, 2021
    Dear
    You Mentioned In the article
    NEC 50.56 Actually It Shall Be NEC 250.56
    • [email protected]
      Dec 12, 2022
      I don’t see 50.56 in the NEC. I don’t see a 250.56 either, what year of the NEC you are using, please advise. Thank you.
  7. Tilak
    Apr 19, 2021
    My question is that what should the value of earthing of residential boarding school hostels and a classroom for all commercial buildings. kindly give your valuable answer so that we can maintain our earthing pits as per given your suggestion.
  8. Alacross
    Apr 07, 2021
    I need to learn
  9. Ezekiel Adeniyi
    Jan 03, 2021
    What should be ground ohms for 10kva solar powered system?
  10. reza
    Aug 21, 2020
    Hi
    that very good
    But I have reach to less than 1 ohm of earth resistance by my special way
  11. Mohammad H. Hamdi
    Jul 22, 2020
    Hi
    can any one tell us the IEC standard for earthing resistance value in general in Oil fields please.
  12. Carlos C. Tamayo Jr.
    Jun 25, 2020
    Seeking your support, appreciate if you could share to me MV Protection coordination study sample.
  13. Garba musa
    Jun 19, 2020
    Sir what is the correct value for earth trasformer
  14. Muhammad Shaheryar
    Apr 06, 2020
    There is no NEC 50.56.
    NEC 250.56 11th edition stated 25 ohms and less.
    NEC 250.56 is excluded from 12th edition
  15. Emeka Chime
    Feb 24, 2020
    In my company, a telecommunication giant in Nigeria, the standard earth resistance value ranges from 2.0 Ohms and below.
    • andy chan
      Feb 27, 2020
      Dear Emeka Chime,
      Please let me know, the standard earth resistance value ranges from 2.0 Ohms, the 2.0 ohms is quote from what authority or international standard?
      Thanks so much
  16. SOJI
    Jan 15, 2020
    Very Educative … Thanks Edvac …!
  17. Ali
    Dec 31, 2019
    is there any reference about the resistance value between clean and dirty earths.
  18. Kimetu
    Dec 07, 2019
    Nice one, very educative, can i get a earth resistance tester and at how much
  19. Satti
    Nov 28, 2019
    I have checked the earth resistance and it’s result is point zero one six seven so kindly tell me about the earth, that is good or not
    Result= .0167
    • Faisal Mohamed
      Oct 23, 2020
      Very good
  20. Eng. Seth Wilson
    Nov 04, 2019
    Hi, meter reads o.23 Ohms, is this good or bad?
    • MOHAMED MOUSTAFA
      Jul 05, 2020
      yes very good
  21. Ugama Albert
    Oct 18, 2019
    I installed a 5kva inverter in a house that has a thunder arrester and it’s earted. But the inverter was still destroyed by thunder. This made me to to run a test on the earthing and was discovered it was 27ohms. How come it was only the inverter that was affected and not the house appliances as well
    • LalitKishor
      Nov 04, 2019
      Because inverter has an isolation transformer and surge circuit inside to avoid cascading the fault current goes.to other appliances
  22. Mahesh
    Oct 04, 2019
    Earthing for Any equipments is Design always request customer for Soil ERT Reports and Design for Equipments or any Kind of Grid.
    Earth Enhance Compound Role is bigger than Metal Part becuse we use Metal to consider Falut Current and Life for Metal but without Good and Quality Compound its not possible.
    Avoid to use any mineral who can Damager or Corrosion your Metal Later .
    India Follow IEC as well IEEE .using CDEGS Software for Desiging Earthing and Lightning
    We has to mentioned Latest Tech Documents is our inquiry or Tender
    M-91-9910398999
  23. Mr G. T Apera
    Sep 04, 2019
    Like to buy Tong earth tester like in the photo please get back to me.
    • Mr G. Apera.
      Sep 02, 2020
      Would like to buy an earth tester (ideal ground resistance meter)
  24. Prashant shalikram pustode
    Aug 24, 2019
    Sir sgp course available ?
  25. Wisdom Ayensu
    Aug 12, 2019
    So what is the correct value for earth?
    • Arif khan
      Apr 20, 2020
      As per standard
      Different application different ohm required
    • MOHAMED MOUSTAFA
      Jul 05, 2020
      from less than 0.5 ohm to 25 ohm as per application ,soil and standards, approximatly
  26. Kafui Sampene
    Jul 31, 2019
    What should be size of lighting arrester pitch
  27. Emmanuel Ephraim Yalley
    Jul 14, 2019
    Please I want to do earthing as my thesis for my 2nd degree project so can you give me some PDF on earthing?
    • zakir hussain
      Oct 09, 2019
      contact me on this email i will send u PDF
  28. Lucky friday
    May 30, 2019
    What damage can lake of earth cause to sound proof generator
  29. Lucky friday
    May 30, 2019
    This is great keep on
  30. Eladio Mosqueda
    Mar 09, 2019
    Dear Edvard,
    Can you please send me if possible the complete IEC standard in WORD or PDF file.
    Thanks and Best Regards.
    • EKIA BONNY
      Aug 11, 2020
      Is there specific ratio for earthing materials like NaCl,charcoal dust etc when it come to residential and industrial earthing?
      I need your help please.
  31. Dr. Md Abdus Salam
    Feb 20, 2019
    The highly recommended value of ground resistance for a residential and commercial area is less than or equal to 1 ohm. You need to use more earth electrode to achieve this value.
  32. Mahmoud Awad
    Jan 05, 2019
    Thanks A lot
  33. JOSE CAMPOS
    Dec 24, 2018
    REALLY, BELLOW 25 OHMS IS ACCEPTABLE (NEC 250-56)
  34. Daham Noaime
    Oct 20, 2018
    very informative , thanks Edvard.
  35. Jorge Chávez
    Aug 07, 2018
    All articles are very helpful Edvard
    Congrats and Thanks a lot
  36. Ojiyovwi Michael
    Aug 02, 2018
    You guys are doing a great job! Very educative. This is electrical engineering made easy and real. keep it up. Thank you.
  37. samer khatib
    Jan 25, 2018
    good day
    can I connect aluminuim wire to the earthing copper rods , i mean are there any problem to make these connection in the present time or in the future .
    i appreciate your reply
  38. Babar
    Nov 22, 2017
    Hey man thats a brief and very informative article.
    i was doing testing in my area, in rocky areas, my lightening resistance was above 300 ohms with 10feet deep cooper plates, where as in other portions it was well below 25ohms, i even hit 5ohm also.
    So we are basically measuring “Potential of Lightening Fall” of a ground. Lower the resistance, higher will be possibility of lightening isnt it?
    • Roy P. Lackey
      Nov 29, 2023
      Babar: In rocky areas I find the best grounding electrodes to be chemical ground rods. If the subsurface ground is solid rock, you would need to bore a hole or cavity into the rock, place the chemical rod into the hole and backfill the hole with “ground enhancement materials. Initially, the ground impedance may test higher than your target impedance but it will fall as the Rod’s internal salts dissolve and form “electrolytic roots” and attach to the undisturbed rock. A good chemical rod vendor would be ERICO.
      Additionally, grounding systems should be designed to “maintain a low impedance on a seasonal basis” instead of initially as installed. Seasonal moisture levels change especially in Clay soils.
  39. Eddy Kasim
    Nov 16, 2017
    Thanks Edvard
  40. solomon
    Jun 19, 2017
    I have a megger earth clamp-on meter, how will I sue it to measure earth resistance value as opposed to conventional earth tester?
  41. Sanele
    Mar 28, 2017
    I am working in substations, I like to know how many ohms should I get when doing earth resistance in the whole substation? Your assistance will be much appreciated. Thank you.
  42. weyih franklin
    Mar 09, 2017
    i will like to know how can one can increase the resistance of his earth system as years runs by.
  43. Aniruddha Moholkar
    Mar 07, 2017
    I m in biomedical field.what must be normal,earth resistance for biomedical equipments.ex for anesthesia workstation.
  44. prakash deo
    Jan 17, 2017
    I am working in Dinshaws Ice cream Nagpur. We have bakery also, I would like to know that what is the value of earthing in Ohms in the earthing points?
  45. ananth
    Jan 02, 2017
    Have you do any earthing tests related to 11 KV motors?
    I have to do earthing tyests with 11 KV motors,
    can you please give some ideas?
    and documents related that?
  46. Tunji
    Nov 25, 2016
    Good enough. Thanks Edvard
  47. trisha gupta
    Aug 22, 2016
    How to measure the value of earth resistance in Multi-Dwelling Unit(Apartments) where neither the earth pit is not accessible, nor the earthing rod?
    Are there any non destructive methods available? By non destructive, I mean without digging?
    • Imran Malik
      Oct 25, 2016
      You may Rap around the ground cable to water pipe. it will reduce the grounding resistance.
  48. suzzanae
    Jun 22, 2016
    Hi, I would like to know whether we can achieve 5 ohm for more than 10 years or not.
    And, can we suggest type of earthing just differentiating wet soil, sand soil or rocky soil without calculation. if any standard thumb rule are there please share .
    Also. LPS for metallic tower and not metallic tower .
  49. gilbert
    May 14, 2016
    may i ask some question reguardimg on bonding of grounding,? how come that it is more efficient my grounding system if i’m goin g to bond the grounding of my lightning arrester in a building grounding? if a high voltgage and current occur cause by a lightning,. do i have a current pass through my equipments which is grounded (connected to a building grounding )???
  50. Jimmy Jones
    Dec 11, 2015
    If I turn off all breakers in my homes main breaker panel and remove the main Neutral Wire from the panel tie point, then run a wire from one unused 120 volt 20 amp breaker to ground the breaker should clear if the ground is sufficient. Right? If it doesn’t clear, then the ground must be over 5 or 6 ohms. I know this is dangerous and I’m not recommending anyone doing it but am I correct in what I’m saying here? I’ve seen people try to obtain this 5 ohms or less ground and never come close to obtaining a low enough resistance reading by itself to clear the breaker.
  51. v.ragu
    Dec 11, 2015
    In my experience we could achieve close to zero that if all the earth rod are interconnected
  52. muhammad salam
    Oct 16, 2015
    whats the domestic,human,and industrial value of grounging
  53. Salman Kamal
    Oct 13, 2015
    Although zero ohm is the most ideal figure, but it is not always the case, in my experience along, there are many solution to make nearby zero, such as carbon and salt arrangement with many earth copper rods connected together and surrounding the premises such as substation. The worst case where you have Stoney ground area with a lack of humidity or source of water.
  54. MIUNSHYA MUSONDA
    Sep 04, 2015
    Hi i want to know the recommended earth resistance value for electrical installation
  55. diolan
    Aug 31, 2015
    hello edvard, the article of the nec is the 250.56 and the value shall be less than 25 ohms. In the article is missin the number “2”.
  56. surya
    May 03, 2015
    so ….we cannot find earth resistance practically
    • Girish R Pillai
      Feb 22, 2016
      We can find earth resistance practically. Earth resistance tester with 3 points or a clamp on type meter will help. Its easy to operate.
  57. joseph
    Apr 21, 2015
    What it’s the purpose of earth megger
  58. Suresh
    Jan 02, 2015
    straight answer to my question. most useful site. Thanq
      You’re welcome Suresh! Straight to the point!
  59. emad hassoun
    Oct 15, 2014
    Very nice shorted ( concetrated information) ….I hope to see more like that ….. thank
  60. godwin
    Oct 15, 2014
    I really like a site like this, were I can reffer some of my engineering questions to. I would like to know how to test a lightning arrestor that is mounted on a mast with a copper tape running down to earth pit?
  61. ghulamsarwar
    Aug 03, 2014
    well this z vry good site for electrical information,,,,v r getting a vry low resistance with copper groundind rod almost 1 ohm……& less than 5 ohm with galvanized steel rod of 19mm dia with 24mm lenght,
  62. Vivek
    Jun 06, 2014
    I have been searching a site like this for quite a long time. I’ve finally discovered the site for all my electrical references. I feel really happy for the good work you do, Edvard. Thanks a lot…
  63. ashraf
    Jun 06, 2014
    Dear Edvard.
    That is so good information , you are professional and I would like to keep in touch with you.
    Sincerely.
    Engineer.
    Bush. Ashraf
  64. ouadi
    May 26, 2014
    RAS
  65. shrikant
    May 10, 2014
    describe 4 point earth resistance measurement method,
    • Girish R Pillai
      Feb 22, 2016
      Its very easy and explained on the meter itself in simple language. To arrange the spikes in a straight line at measured intervals. Apply current by pressing the push button. Note the reading and calculate based on the formula which is inversely proportional to the distance between spikes.
  66. Raj
    Apr 24, 2014
    In house we get 7 to 5 ohms.
  67. ashish
    Feb 02, 2014
    my think bildup
  68. Sohail Khan
    Dec 29, 2013
    Nice information about earthing resistance….
  69. iwak
    Dec 25, 2013
    where i can informasi accurate troubleshooting electrical,i m from indonesia,write english no good
    • jaweed
      Aug 03, 2019
      dear sir,
      Good morning ,we use CA-6417 Ground Test Meter,during testing meter display showing LOOP(blinking) & 0.23 Ohm,my Question is what the meaning LOOP,
      please explain grounding is or bad.if ground is tell me solution your reply highly appreciated.
Leave a Reply to Prashant shalikram pustode