Electric motors & power factor influence

A low power factor causes poor system efficiency. The total apparent power must be supplied by the electric utility. With a low power factor, or a high-kilovar component, additional generating losses occur throughout the system.

Why Raise the Power Factor? The Basics You Should Know.
Why Raise the Power Factor? The Basics You Should Know. (photo credit: .see-tech.com)

Figures 1 and 2 below illustrate the effect of the power factor on generator and transformer capacity.

To discourage low-power factor loads, most utilities impose some form of penalty or charge in their electric power rate structure for a low power factor.

When the power factor is improved by installing power capacitors or synchronous motors, several savings are made:

  1. A high power factor eliminates the utility penalty charge. This charge may be a separate charge for a low power factor or an adjustment to the kilowatt demand charge.
  2. A high power factor reduces the load on transformers and distribution equipment.
  3. A high power factor decreases the I2R losses in transformers, distribution cable, and other equipment, resulting in a direct saving of kilowatt-hour power consumption.
  4. A high power factor helps stabilize the system voltage.
Power factor effect on generator capacity
Figure 1 – Power factor effect on generator capacity
Power factor effect on transformer capacity
Figure 2 – Power factor effect on transformer capacity

So, how to improve power factor?

To improve the power factor for a given load, the reactive load component (kvar) must be reduced.

This component of reactive power lags the power component (kW input) by 90 electrical degrees, so that one way to reduce the effect of this component is to introduce a reactive power component that leads the power component by 90 electrical degrees.

This can be accomplished by the use of a power capacitor, as illustrated in the power diagram in Figure 3, resulting in a net decrease in the angle θ or an increase in the power factor.

Vector diagram of power input with a power factor correction
Figure 3 – Vector diagram of power input with a power factor correction

Several methods are used to improve the power factor in a system installation. One method that can be employed in large systems is to use synchronous motors to drive low-speed loads that require continuous operation.

A typical application for a synchronous motor is driving a low-speed air compressor, which provides process compressed air for the plant.

The synchronous motor is adjusted to operate at a leading power factor and thus provide leading kilovars to offset the lagging kilovar of inductive-type loads such as induction motors.

Synchronous motors are usually designed to operate at an 80% leading power factor and to draw current that leads the line voltage rather than lags it, as is the case with induction motors and transformers.

For example, consider a load of 2000 kW at a 70% lagging power factor. The utilization of a 200-hp synchronous motor operating at an 80% leading power factor will increase the overall system power factor from 70% lagging to 85% lagging.


Using power capacitors

The more popular method of improving the power factor on low voltage distribution systems is to use power capacitors to supply the leading reactive power required.

The amount and location of the corrective capacitance must be determined from a survey of the distribution system and the source of the low-power factor loads.

In addition, the total initial cost and payback time of the capacitor installation must be considered.

To reduce the system losses, the power factor correction capacitors should be electrically located as close to the low-power factor loads as possible. In some cases, the capacitors can be located at a particular power feeder. In other cases, with large horsepower motors, the capacitors can be connected as close to the motor terminals as possible.

The power factor capacitors are connected across the power lines in parallel with the low-power factor load. The number of kilovars of capacitors required depends on the power factor without correction and the desired corrected value of the power factor.

The power factor and kilovars without correction can be determined by measuring the power factor, line amperes, and line voltage at the point of correction.

For a three-phase system,

kVA, kvar, kW

Or the line kilowatts, line amperes, and line voltage can be measured. Then,

kVA, PF and kvar

The capacitive kilovars required to raise the system to the desired power factor can be calculated as follows:

capacitive kilovars

where PF is the desired power factor.


Let’s take an example…

For example, consider a 1000-kW load with a 60% power factor, which one wishes to correct to 90%:

1000-kW load with a 60% power factor

Tables such as Table 1 have been developed and are available from most power capacitor manufacturers to simplify this calculation. Table 1 provides a multiplier to be applied to the kilowatt load to determine the capacitive kilovars required to obtain the desired corrected power factor.

Consider the same 1000-kW load with a 60% power factor which one wishes to correct to 90%.

Table 1 – Power Factor Correction Factors

Power Factor Correction Factors
Table 1 – Power Factor Correction Factors

From Table 1, for the existing power factor (60%) and the corrected power factor (90%), the power factor correction factor is 0.849. Thus, the number of kilovars of capacitance required is 1000 × 0.849 = 849 kvar.

Let us verify this calculation:

Capacitance calculations

Adding corrective kilovars

Over the years, there have been several guidelines used for the selection of induction motor power factor correction capacitors. Three of these guidelines are as follows:

  1. Add corrective kilovars of capacitors equal to 90% of the motor no-load kilovolt-amperes.
  2. Add corrective kilovars of capacitors equal to 100% of the motor no-load kilovolt-amperes.
  3. Add corrective kilovars of capacitors equal to 50% of the motor full-load kilovolt-amperes.


Table 2 is a comparison of these methods of selecting correction capacitors for some typical four-pole, 1800-rpm induction motors.

Table 2 – Comparison of Power Factor Correction Methods

Comparison of Power Factor Correction Methods
Table 2 – Comparison of Power Factor Correction Methods

The question is: What is a typical motor in regard to power factor?

Figure 4 shows the variation in full-load power factor for standard four-pole, 1800-rpm induction motors. Figure 4 is based on published data from 10 electric motor manufacturers.

Power factor Nema design B, 1800-rpm induction motors
Figure 4 – Power factor Nema design B, 1800-rpm induction motors

The difference in the full-load power factor for a specific horsepower rating can vary by 5 to 15 points. Therefore, it is best to know the power factor information on the specific motors requiring power factor correction.

The no-load methods of selecting correction capacitors are conservative and increase the corrected power factor to 95% or higher. However, the no-load information is not readily available. In contrast, the full-load power factor and efficiency are generally available either as published literature or on the motor nameplate.

These data can be used to calculate the motor power factor and input kilowatt-amperes.

The use of the 50% full-load kilowatt-amperes to determine the corrective kilovars generally results in a corrected power factor of 0.99 or better to a slightly leading power factor. This method should be used with caution if the motor is not operating at full rated load.

Under partial-load conditions, the corrected power factor can be over 0.90 leading. The higher the horsepower of the motor, the more likely it is that the corrected power factor can be leading at partial loads.

A partial motor load is not an unusual condition.

Studies indicate that the average load on induction motors rated 125 hp and larger ranges from 50 to 85% of full-load rating. For 1800-rpm induction motors the power factor at 50% load is usually 0.07 to 0.14 points lower than the power factor at full load.

If the capacitor correction is not used to supply kilovars for other uncorrected motors on the same circuit, a value lower than 50% of the full-load input kilovolt-amperes should be used for the correction kilovars.


NEMA Recommendations

In the application of power factor correction capacitors at the motor location, NEMA recommends the following procedure based on the published or nameplate data for the electric motor:


Procedure #1

The approximately full-load power factor can be calculated from published or nameplate data as follows:

Power factor formulae

where:

  • PF = per unit power factor at full load (per unit PF = percent PF/100)
  • hp = rated horsepower
  • E = rated voltage
  • I = rated current
  • Eff = per unit nominal full-load efficiency from published data or as marked on the motor nameplate (per unit Eff = percent Eff/100)

Procedure #2

For safety reasons, it is generally better to improve the power factor for multiple loads as a part of the plant distribution system.

In those cases in which local codes or other circumstances require improving the power factor of an individual motor, the kilovar rating of the improvement capacitor can be calculated as follows:

kvar formulae

where

  • kvar = rating of a three-phase power factor improvement capacitor
  • PFi = improved per unit power factor for the motor-capacitor combination

Procedure #3

In some cases, it may be desirable to determine the resultant power factor PFi, where the power factor improvement capacitor selected within the maximum safe value specified by the motor manufacturer is known.

The resultant full-load power factor PFi can be calculated from the following:

PFi formulae

Warning! In no case should power factor improvement capacitors be applied in ratings exceeding the maximum safe value specified by the motor manufacturer. Excessive improvement may cause over-excitation, resulting in high transient voltages, currents, and torques, which can increase safety hazards to personnel and cause possible damage to the motor or to the driven equipment.

The level to which the power factor should be improved depends on the economic payback in terms of the electric utility power factor penalty requirements and the system energy saved because of lower losses.

In addition, the characteristic of the motor load must be considered. If the motor load is a cyclical load that varies from the rated load to a light load, the value of corrective kilovar capacitance should not result in a leading power factor at light loads.

To avoid this possibility, NEMA recommends that the maximum value of the corrective kilovars added be less than the motor no-load kilovar requirement by approximately 10%.

Thus, Maximum capacitor kvar for three-phase motors:

Maximum capacitor kvar for three-phase motors

where:

  • INL = motor no-load line current
  • V = motor line voltage

For example, consider a 50-hp, 1800-rpm induction motor operating on a 230-V, three-phase, 60-Hz power system.

Table 3 shows the performance of this motor at various loads without power factor correction. Table 4 shows the full-load performance with various values of correction capacitor kilovars, including 100% of the no-load kilovolt-amperes (13.7 kvar) and 50% of the full-load kilovolt-amperes (23.7 kvar).

Table 3 – Induction Motor Performance Without Power Factor Correction

Induction Motor Performance Without Power Factor Correction
Table 3 – Induction Motor Performance Without Power Factor Correction

Table 4 – Induction Motor and Capacitor Performance with Power Factor Correction at Full Load

Induction Motor and Capacitor Performance with Power Factor Correction at Full Load
Table 4 – Induction Motor and Capacitor Performance with Power Factor Correction at Full Load

These values of kilovars correct the power factor to 0.97 and unity, respectively.

Based on 4000 hr/yr operation at 5¢/kWh for electric energy, a correction to unity power factor could result in a saving in energy costs of $70/yr. The combined motor–capacitor performance at partial loads is shown in Table 5.

Note that at partial loads with the higher values of corrective kilovars the power factor can be very leading.

Table 5 – Induction Motor and Capacitor Performance with Power Factor Correction at Various Loads

Induction Motor and Capacitor Performance with Power Factor Correction at Various Loads
Table 5 – Induction Motor and Capacitor Performance with Power Factor Correction at Various Loads

Figure 5 shows the comparison of the corrected and uncorrected power factor at various level of kilovar correction for the 50-hp induction motor.

WARNING! The high level of power factor correction should be avoided if the motor is going to be operating at partial loads and the capacitors are connected directly to the motor terminals.

Power factor of 50-hp induction motor with various levels of kilovar correction: (1) no correction, (2) 12-kvar correction, (3) 13.7-kvar correction, (4) 23.7-kvar correction
Figure 5 – Power factor of 50-hp induction motor with various levels of kilovar correction: (1) no correction, (2) 12-kvar correction, (3) 13.7-kvar correction, (4) 23.7-kvar correction

The application of capacitor kilovars up to the no-load kilowatt-amperes results in a lagging power factor for all load conditions.

The National Electric Code (NEC) has removed any restrictions on the size of power factor correction capacitors applied to induction motor circuits. This places the responsibility on plant electrical engineers to select the power factor correction strategies that best suit their plant operations.

Reference //  Energy Efficient electric motors by Marlin O. Thurston; Department of Electrical Engineering The Ohio State University Columbus, Ohio

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
author-pic

Edvard Csanyi

Electrical engineer, programmer and founder of EEP. Highly specialized for design of LV/MV switchgears and LV high power busbar trunking (<6300A) in power substations, commercial buildings and industry facilities. Professional in AutoCAD programming.

14 Comments


  1. Agbezouke Koffi Richard
    May 18, 2022

    Thanks for a comprehensive explanation.


  2. REHAMAN SAYYED
    Aug 10, 2019

    Nice explanation and understanding


  3. Shafik Ahmad
    Jul 07, 2019

    Explained power factor and its effect in most simplest way.


  4. Julius Eclarino
    Mar 17, 2019

    Nice presentation very informative. Power factor really a big help in power system specially in system where inductive loads are significant in numbers.

    I would like to share my observations about the impact of solar power in-feed connection in power factor. Our system is 400V/230V, 60hz capacitor banks are already in place and most of the time, average pf will not fall below 95% both day and night operation.

    There was this solar project that is connected in Low voltage side of the system. The solar energy setup would be: solar cell -> inverter -> inverter panel -> low voltage switch gear. My observation during daytime, power factor decreases from 95% to 20% depending on the harvest of solar power. Power factor will increase to 95% when solar energy is not there. Do you have any case study regarding this one?

    Thank you


    • Colonel SP Saini
      Jun 01, 2020

      Solar Plant is capable of feeding reactive power in case load demands or in case of poor GRID power factor. Thus pooer power factor in case Solar Power Plant is on, is not possible. There may be some other reason for poor power factor.


      • Colonel SP Saini
        Jun 01, 2020

        Solar PV Plant is designed to provide power at 30 degree leading to 30 degree lagging depending upon requirement and Grid conditions at load end.


        • Alhadi Abusalah
          Sep 16, 2021

          Clear and good explanation of pf issues


  5. Aman gupta
    Aug 23, 2018

    It really helps


  6. JAIROS KATAMBI
    Aug 19, 2018

    Thanks for the wonderful and well articulated information on power factor collection.


  7. Andrzej
    Jun 07, 2018

    Would you please write some comments about power factor when VSD is applied.


  8. Kithsiri Kularathna
    Jun 07, 2018

    Please ex plane How to buildup harmonic(Voltage & Current) in LV system & how to reduce that harmonic(Current harmonic & Voltage Harmonic), Kindly request If you have basic cause material for that please send me, Thanks.


  9. Shubham gautam
    Jun 07, 2018

    Concept clear of power factor


  10. Joshua
    Jun 07, 2018

    Thanks


  11. Mwape chileshe
    Jun 06, 2018

    Great piece of information well explained

Leave a Reply to Colonel SP Saini

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

6  ×    =  thirty

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

Subscribe to Weekly Newsletter

Subscribe to our Weekly Digest newsletter and receive free updates on new technical articles, video courses and guides (PDF).
EEP Academy Courses - A hand crafted cutting-edge electrical engineering knowledge