Home / Technical Articles / Calculating Max. Demand Kilovolt-Amperes and Required Cable Current Rating
A building site and electrical equipment
A building site is to have the following electrical equipment available for use:
  • Tower crane, electric motors totalling 75 kW at 415 V;
  • Sump pump, 5 kW at 240 V;
  • 60 tungsten lamps of 100 W each at 240 V;
  • 12 flood lamps of 400 W each at 240 V;
  • 20 hand tools of 400 W at 110 V.
To calculate //
  1. Find the total kilovolt-amperes to be supplied to the site if the power factor of all rotary equipment is 0.8.
  2. Find the electrical current rating for the incoming supply cable to the site.
  3. Estimate the cost of electricity consumed on the site during a 12-month contract.
Ok, let’s do it…
For rotating machinery, formulae for power in Volt Amperes [VA] goes like this:
Power [volt-amperes]
For single-phase current:
Single-phase current
For three-phase current:
Three-phase current
The results of the power calculations are given in Table 1 below. The answers required are as follows.
1. The total input power kilovolt-amperes required for site is 120.8 kVA
2. The incoming supply cable capacity at 415 volt, three-phase, 50 Hz required is:
Current
This is the input current to the site at the voltage of that cable. This is not the same as a total of the currents calculated in Table 1 as these larger numbers only appear at their reduced voltages in the relevant sub-circuits.
3. Assume that the crane, pump and tools are running for 25% of an 8-h working day, 5 days per week for 48 weeks, 20 of the tungsten lamps are for security lighting 16 h every night, and the remaining 40 tungsten lamps and the flood lamps are used for 3 h per day, 5 days per week for the winter period of 20 weeks.
The crane, pump and tools are working for:
Hours formula
The security lamps are working for:
Hours formula
The other lamps are working for:
Hours formula
Table 1 – Building site plant schedule
EquipmentPower (kW)NumberkWkVAVA
Tower Crane7517593.75415130.4
Sump Pump5156.2524026
Lamps0.1606624025
Flood Lamps0.4124.84.824020
Hand Tools0.42081011090.9
Total //98.8120.8n.a.n.a.
Table 2 – Building site energy use
EquipmentPower (kW)NumberTime (h)Energy (kWh)
Tower Crane75148036000
Sump Pump514802400
Tungsten lamps, security Lamps0.120582411648
Lamps0.1403001200
Flood Lamps0.4123001440
Hand Tools0.4204803840
Total Power Used //56528
The total energy used by the systems is found from:
kWh = number of appliances × kW per appliance × operation hours as shown in Table 2.
If electricity costs 8 p per unit (kWh) then the estimated cost for the 1-year contract will be:
Electricity cost
Reference: Building Services Engineering // Electrical Installations – David V. Chadderton (Purchase paperback from Amazon)
18 Comments
  1. Sanjay
    Apr 21, 2022
    I need to know how to calculate MD
  2. Chizzy
    Sep 03, 2019
    Thanks alot.. I’m most grateful
  3. Vincent Torry
    Dec 17, 2018
    Thank You so much, its really helpful.
  4. J d patel
    Mar 01, 2018
    How to calculate MD in electrical language.
  5. Rohit subramanian
    Mar 03, 2017
    I have problem in one of the site where the connecting load is High HP pump -150 and 60 with 500kva transformer connected .
    the MD is 185 connected obtained but the ideal time is so high that power factor is getting low checked out the parameters additional 1.5KVAR given for the grid than also the power factor is not getting maintained.
    last month MD shooted up to 193.4 KVA but the running of the plant was minimal .
    Help out in this regards
  6. ALI
    Jan 18, 2017
    hay i am doing analysis on base of MDI penalty can anyone please tell me that how it is calculated. in bill i find readings like this
    PRV CUMM MDI 98 PRS CUMM MDI 104 MDI 6
    what does this mean….
  7. magdy
    Aug 17, 2015
    we just start a construction of abig project at ajyad of mekkah saudi arabia we wanna make calculation of the total power needed for service using demand and load factor please tel me me how to compute the demand factor
  8. Munaf
    Aug 15, 2015
    Thank you for the information
  9. K.Ruju
    Mar 04, 2015
    Thanks for the Information
  10. jesus g
    Feb 21, 2015
  11. Loum Peter
    Feb 08, 2015
    I’m so sorry i had forgotten the principle of the power triangle so sorry really the 93.75kva for the crane is correct.
  12. Bimal
    Feb 08, 2015
    Nice good and very helpful
  13. Thomas
    Feb 07, 2015
    How about the power consumption for testing& commissioning?
  14. Loum Peter
    Feb 06, 2015
    Thanks for your information, but one think..for three phase , power W=1.732xV(line)xI(line)xPF no? if so that means VA =W/(1.732×0.8) and the KVA for the crane would be 54.13KVA….
    • jesus perez
      Feb 07, 2015
      No. Active power (W) is equal to VA x power factor
  15. sandar
    Feb 05, 2015
    Thanks u for ur information
  16. Anthony Uwadiae
    Feb 03, 2015
    Thanks for the information.
  17. Bonginkosi
    Feb 03, 2015
    Thank you Edvard Csanyi for an informative and summarized example.
    it assisted me in a project I am doing now.
    I keep reading your articles, these are very helpful articles
    the whole page is very useful, keep up the good work
Leave a Reply to Bimal
8  ×    =  16
