Inputs for Coordination Calculation

A 440 V 60 Hz switchboard feeds a 4-wire distribution board for small loads such as socket outlets. The switchboard has a fault making capacity of 100kA rms. After applying diversity factors to the loads the total load current is 90 A. Moulded case circuit breakers (MCCBs) rated at 16 A and 32 A are to be used for the loads.

Example for Coordination of Cascaded Circuit Breakers
Example for Coordination of Cascaded Circuit Breakers (on photo: Low voltage SIEMENS SIKUS 1600 power distribution board; credit: DirectIndustry.com)

The installation will use cables having copper conductors and XLPE insulation. The cable from the switchboard to the distribution board is 20 metres in length.

A typical load cable is 15 metres in length and will carry a current of 29 A at a power factor of 0.85 lagging.


Let’s dive into solution!

1. Choose the upstream MCCB at the switchboard and its settings

From a manufacturer’s data sheet a 125 A MCCB with an adjustable 100 A thermal release is chosen. The thermal release is set to 90 A to match the total load.


2. Choose the incoming feeder cable

From a manufacturer’s data sheet several cables can be compared for the same ambient conditions and laying arrangements. Their details are:

  • 50 mm2 cable, maximum current 124 A, R = 0.492, X = 0.110 ohms/km.
  • 70 mm2 cable, maximum current 159 A, R = 0.340, X = 0.106 ohms/km.
  • 95 mm2 cable, maximum current 193 A, R = 0.247, X = 0.093 ohms/km.
The 70 mm2 cable is chosen since the rating of the 50 mm2 cable is just too low.

Go back to Index ↑


3. Choose the downstream load MCCB and its settings

From a manufacturer’s data sheet a 32 A MCCB with an adjustable 32 A thermal release is chosen. The thermal release is set to 29 A to match its load.


4. Find the upstream fault source impedance

For a prospective symmetrical fault current of 100 kA rms the upstream fault source impedance Zup is:

Upstream fault source impedance


Go back to Index ↑


5. Find the cut-off, or let-through, current from the switchboard

From a manufacturer’s data sheet a 125 A MCCB has a let-through current Ip of 25 kA peak for a prospective fault current Is of 100 kArms.


6.  Find the impedance of the incoming cable

The impedance Zc1 of the incoming cable is:

Impedance of the incoming cable


Go back to Index ↑


7. Find the impedance of the load cable

The impedance Zc2 of the incoming cable is:

From a manufacturer’s data sheet several cables can be compared for the same ambient conditions and laying arrangements. Their details are:

  • 6 mm2 cable, maximum current 33.8 A, R = 3.91, X = 0.130 ohms/km.
  • 10 mm2 cable, maximum current 46.7 A, R = 2.31, X = 0.126 ohms/km.
The 6 mm2 cable is chosen provisionally, since its rating is above the 32 A rating of the MCCB that feeds it.

The impedance Zc2 of the load cable is:

Impedance of the load cable


Go back to Index ↑


8. Find the fault current at the distribution board, point B

From a manufacturer’s data sheet the contact impedance data for low voltage MCCBs are:

MCCB
(Rating in Amps)
Resistance
(in Ohms)
Reactanse
(in Ohms at 60Hz)
160.01neglect
200.008neglect
250.0065neglect
320.0050.000009
500.00270.000016
630.0020.000025
800.00140.000042
1000.00110.00007
1250.00080.0001
1600.000550.00015
2000.00040.0002
2500.000290.00027
3200.00020.0004

Hence the upstream MCCB impedance Zm1 is 0.0008 + j 0.0001 ohms. Therefore the fault impedance Zfb is:

Fault impedance

The fault making current Ifb is:

Fault making current

Where Vp is the line-to-neutral voltage. Locate the point R for 26,195 A on the prospective curve in Figure 1.

Go back to Index ↑


9. Find the fault current at the beginning of the load cable, point C

Hence the downstream MCCB impedance Zm2 is 0.005+j0.000009 ohms. Add this to Zfb to give the fault impedance Zfc as:

Fault current at the beginning of the load cable

The fault making current Ifc is:

Fault making current

Locate the point S for 17,443 A on the prospective curve in Figure 1.

Go back to Index ↑


10. Find the fault current at the end of the load cable, point D

Coordination of MCCBs at a distribution board
Figure 1 – Coordination of MCCBs at a distribution board

Add Zc2 to Zfc to give the fault impedance Zfd as:

Fault impedance

The fault making current Ifd is:

Fault making current

Locate the point U for 3473 A on the prospective curve in Figure 1.

Go back to Index ↑


11. Check the peak making capacity and peak let-through capacity of the MCCBs chosen above

The following manufacturer’s data are typical for 125 A and 32 A MCCBs:

MCCB RatingMaking capacityLet-through capacity
kApeak (cut-off)
kArmskApeak
 32 A95209 ***6.0
 125 A132 290 ***25.0

*** Approximate values of the doubling factor taken to be 2.2

Hence the peak making capacity of the 32 A MCCB is well in excess of the let-through peak current of the 125 A MCCB.

Go back to Index ↑


12. Find the highest I2t value for the upstream MCCB

Locate two points P and Q on the curve of the upstream MCCB as follows,

PointCurrent in p.u.Current in AmpsTime in secondsI2t
P144066989016.0
Q60217,4500.0016487204.0

Hence I2t at P exceeds that at Q.


13. Calculate a suitable size for the load cable to satisfy the I2t duty

For XLPE cables the ‘k factor’ for the I2t is 143. The cross-sectional area A is:

Suitable size for the load cable

The next standard cross-sectional area is 10 mm2.

Go back to Index ↑


14. Calculate the volt-drop in the load cable

The usual limit to volt-drop in three-phase cables feeding static loads is 2.5% at full load.

Volt drop

Where, Iflc = 29 A, L = 15 m and φ = 54.5495 degrees. For a 6 mm2 cable the volt-drop is found to be:

Volt drop

which is well within the limit of 2.5%.

Go back to Index ↑


15. Select the largest conductor size from the above calculations

Comparing the conductor sizes found in 13. and 14. gives the larger as 10 mm2, and this size should be used. Revise the calculation of the fault current Ifd. The impedance Zc2 of the load cable is:

Impedance Zc2

Add Zc2 to Zfc to give the fault impedance Zfd as:

Fault impedance

The fault making current Ifd is:

Fault making current


Go back to Index ↑


16. Plot the results

The results are plotted in Figure 1.

Coordination of MCCBs at a distribution board
Figure 1 – Coordination of MCCBs at a distribution board

Refrence // Switchgear and Motor Control Centres – Handbook of Electrical Engineering: For Practitioners in the Oil, Gas and Petrochemical Industry by Alan L. Sheldrake (Download here)

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Edvard Csanyi - Author at EEP-Electrical Engineering Portal

Edvard Csanyi

Hi, I'm an electrical engineer, programmer and founder of EEP - Electrical Engineering Portal. I worked twelve years at Schneider Electric in the position of technical support for low- and medium-voltage projects and the design of busbar trunking systems.

I'm highly specialized in the design of LV/MV switchgear and low-voltage, high-power busbar trunking (<6300A) in substations, commercial buildings and industry facilities. I'm also a professional in AutoCAD programming.

Profile: Edvard Csanyi

One Comment


  1. Ismail
    Jul 22, 2015

    Hello, just a small question, in the introduction the main cable size is given as 20m so why was it used as 25m to calculate the impedance in number 6 ?

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.
This whitepaper by OMICRON explores the fundamental shift in substation automation testing from hardware-dependent setups to virtualized, software-defined verification.