Home / Technical Articles / High voltage station – Design, construction and commissioning process
High Voltage Station – 3 Main Processes
Having selected the right site location for high voltage station, the design construction and commissioning process would broadly follow the steps shown in Figure 1. Recent trends in utilities have been toward sourcing design and construction of HV stations through competitive bidding process to ensure capital efficiency and labor productivity.
High voltage station – Design, construction and commissioning process (on photo: Construction of 400 kV SF6 switching station; credit: gruner.ch)
Now, let’s start discussing the three main processes:
  1. Design
  2. Construction
  3. Commissioning
1. HV Station Design
Now the final detailed designs can be developed along with all the drawings necessary for construction. The electrical equipment and all the other materials can now be ordered and detailed schedules for all disciplines negotiated. Final manpower forecasts must be developed and coordinated with other business units.
It is imperative that all stakeholders be aware of the design details and understand what needs to be built and by when to meet the in-service date.
Once the designs are completed and the drawings published, the remaining permits can be obtained.
Establishment of a new substation
Figure 1 – Establishment of a new substation
The following can be used as a guide for various design elements:
Basic Layout
  • Stage development diagram
  • Bus configuration to meet single line requirements
  • Location of major equipment and steel structures based on single line diagram
  • General concept of HV station
  • Electrical and safety clearances
  • Ultimate stage
Design
  • Site Preparation – Drainage and erosion, earth work, roads and access, and fencing
  • Foundations – Soils, concrete design, and pile design
  • Structures – Materials, finishes, and corrosion control
  • Buildings
    • Control, metering, relaying, and annunciation buildings — types such as masonry, prefabricated, etc.
    • Metalclad switchgear buildings
    • GIS buildings
  • Mechanical Systems
    • HVAC
    • Sound enclosure ventilation
    • Metalclad switchgear or GIS buildings ventilation
    • Fire detection and protection
    • Oil sensing and spill prevention
  • Buswork
    • Rigid buses
    • Strain conductors – swing, bundle collapse
    • Ampacity
    • Connections
    • Phase spacing
    • Short circuit forces
  • Insulation – Basic impulse level and switching impulse level
  • HV Station Insulators
    • Porcelain post type insulators
    • Resistance graded insulators
    • Polymeric post insulators
    • Subtation insulator hardware
    • Selection of subtation insulator – TR – ANSI and CSA standard
    • Pollution of insulators – pollution levels and selection of leakage distance
  • Suspension Insulators
    • Characteristics
    • Porcelain suspension insulators
    • Polymeric suspension insulators
    • Suspension insulators hardware
    • Selection of suspension insulators
  • Clearances
    • Electrical clearances
    • Safety clearances
  • Overvoltages
    • Atmospheric and switching overvoltages
    • Overvoltage protection – pipe and rod gaps, surge arresters
    • Atmospheric overvoltage protection – lightning protection (skywires, lightning rods)
  • Grounding
    • Function of grounding system
    • Step, touch, mesh and transferred voltages
    • Allowable limits of body current
    • Allowable limits of step and touch voltages
    • Soil resistivity
    • General design guidelines
  • Neutral Systems
    • Background of power system grounding
    • Three and four wire systems
    • HV and LV neutral systems
    • Design of neutral systems
  • HV Station Security
    • Physical security
    • Electronic security
Go back to HV station processes ↑
2. HV Station Construction
With permits in hand and drawings published, the construction of the substation can begin. Site logistics and housekeeping can have a significant impact on the acceptance of the facility.
Parking for construction personnel, traffic routing, truck activity, trailers, fencing, and mud and dirt control along with trash and noise can be major irritations for neighbors, so attention to these details is essential for achieving community acceptance.
All the civil, electrical, and electronic systems are installed at this time. Proper attention should also be paid to site security during the construction phase not only to safeguard the material and equipment, but also to protect the public.
3. HV Station Commissioning
Once construction is complete, testing of various systems can commence and all punch-list items addressed. To avoid duplication of testing, it is recommended to develop an inspection, testing and acceptance plan.
Elements of inspection, testing and acceptance plan include:
  1. Factory acceptance tests (FAT)
  2. Product verification plan (PVP)
  3. Site delivery acceptance test (SDAT)
  4. Site acceptance tests (SAT)
Final tests of the completed substation in a partially energized environment to determine acceptability and conformance to customer requirements under conditions as close as possible to normal operation conditions will finalize the in-service tests and turn-over to operations.
Environmental cleanup must be undertaken and final landscaping can be installed! Note that, depending upon the species of plants involved, it may be prudent to delay final landscaping until a more favorable season in order to ensure optimal survival of the foliage.
Public relations personnel can make the residents and community leaders aware that the project is complete and the station can be made functional and turned over to the operating staff.
Reference: The Electric Power Engineering Handbook by Grigsby, L.L (Get it from Amazon)
  1. meaghan
    Feb 04, 2021
    Is there much work available in this space for subcontractors?
  2. Thabiso
    Nov 18, 2016
    this is a great site ..
  3. doukhane
    Nov 14, 2016
    merci
  4. xin
    Nov 14, 2016
    I would say there is one major item missing, that is the specification and purchase of main circuit apparatus and auxiliary power systems.
Leave a Reply to doukhane
32  ⁄    =  32