Home / Technical Articles / On-site transformer diagnostic measurements: The art of troubleshooting and maintenance
Transformer measurements
Transformer life management requires a portfolio of the different kinds of on-site electrical tests to be performed. This is where things get complicated. The purposes for performing these tests include fingerprint measurements of new transformers to characterize the initial status, routine tests (periodic checks) for observing trends, monitoring as an early “warning system”, and tests for troubleshooting and fault location.
On-site transformer diagnostic measurements: The art of troubleshooting and maintenance (on photo: Maintenance engineer preparing connections for performing dielectric frequency response (DFR) analysis)
Sometimes it is hard for maintenance engineers to correctly interpret contradictory data taken from various transformer measurements. This could potentially lead to making bad decisions which could cost a lot, and this is something that should be avoided.
This technical article presents a breakdown of the most important standard and special on-site transformer tests and measurements along with a short explanation of the test method, detectable failures, failure indication, reference and correct interpretation of measurement results.
The main targets of on-site tests are:
  1. Control of the ageing performance of insulating oil and the solid insulation due to dielectric and thermal aging.
  2. Discrimination of failure type as thermal or dielectric.
  3. Measurement, localization and assessment of partial discharge activity.
  4. Control of mechanical changes due to dynamic impacts.
  5. Trending of moisture absorption and ageing of both the liquid and the solid insulation.
This article gives a summary of the typical problems that may be detected with electrical tests and dissolved gas analyses.
  1. Basic Transformer Measurements:
    1. Winding Ratio
    2. Winding Resistance
    3. Magnetising Current
    4. Capacitance and Dielectric Dissipation Factor (or Power Factor)
      1. Bushing Diagnostics
    5. Leakage Reactance (Short-Circuit Impedance)
    6. Insulation Resistance
    7. Core Grounding
  2. Special Transformer Measurements:
    1. Frequency Response Analysis (FRA)
    2. Polarization/Depolarization Current (PDC) Method Detectable Failures
    3. Frequency Domain Spectroscopy (FDS)
    4. Electrical Method for Partial Discharge (PD) Measurement
    5. Acoustic Partial Discharge (PD) Measurement
    6. Partial Discharge (PD) Measurement using UHF Technology
    7. Frequency Response of the Stray Losses (FRSL)
    8. Recovery Voltage Method (RVM)
  3. Summary Table
1.1 Winding Ratio
Detectable Failures: – Shorted winding sections or turns.
Indication: – Buchholz relay tripping OLTC repair.
Test Method: An AC source is connected to each phase of the HV winding with all other windings open-circuited. The source voltages across the HV winding and across the LV winding are measured.
Reference: Test report or rating plate, comparison of phases.
Interpretation: Measurement should be ± 0.5% of the nameplate values.
Comments and Suggestions:
  1. Some test equipment may allow magnetising current to be measured concurrently.
  2. Avoid performing winding resistance tests before the winding ratio measurement is carried out. The residual flux could impact the measurement.
  3. The ratio test is normally performed following internal work on the transformer involving disconnections of any leads, especially the OLTC.
Suggested Reading – My worst experience in testing and commissioning power transformers (and how I fixed things up)
1.2 Winding Resistance
Detectable Failures: Contact problems on the tap selector, contact problems on the diverter switch, broken conductors, broken parallel strands, shorted winding disks, shorted winding layers, poor bushing connections.
Indication: High internal temperatures, normally indicated by the DGA.
Test Method: A constant current source is used to feed a DC current into the winding. The test current and the voltage across the winding are measured and the resistance value is calculated.
The accuracy of the equipment should guarantee that differences of 1% or even lower can be detected. Since the winding resistances are small, the test set should be connected in 4-wire technology. A relatively high no-load voltage enables a quick saturation of the core and a fast reaching of the stationary final value.
It is recommended to measure the resistance for all taps of the OLTC. The resistance values should be corrected to 75°C according to IEC 60076 Part 1.
Reference: Test report of the manufacturer, fingerprint measurements.
Interpretation: The measured winding resistance should not differ more than about 1% compared to the factory test report if the winding temperature at measurement conditions is corrected to the factory conditions.
Difference between phases usually less than 2-3%. Comparison between HV and LV resistance is usually in the order of the square of the winding ratio when losses are balanced between HV and LV.
In comparison to the LV winding, the resistance of the HV winding is much higher. Therefore identification of contact problems can be less sensitive on the HV side than the LV side.
If the LV windings have very low resistance values, in the order of a few mΩ, it can be helpful to use the HV winding of the same limb in serial connection to get faster stabilization of the measurement current. The time needed to get stable readings can be in the order of tens of minutes for very low resistance values.
Suggested Guide – Measurements Of Transformer Winding Resistance For Diagnostic Purposes
1.3 Magnetising Current
Detectable Failures:Core faults (shorted laminations), shorted turns or winding parts.
Indication:Buchholz relay tripping or DGA.
Test Method:An AC source is connected to each phase of the HV winding with all other windings open-circuited. The source voltage across the HV winding and the source current are measured. If possible, the phase angle should also be measured.
Reference:Comparison of phases, fingerprint measurements.
Interpretation:Normally the outer phases have similar values within 5%. The current in the middle phase can be up to 30% lower.
  1. Some test equipment may allow the winding ratio to be measured concurrently.
  2. Magnetising current at rated voltage is only 0.1 – 0.3 % of rated current. Voltage dependency of magnetising current means comparison testing must use the same test voltage and tap position.
  3. Avoid performing winding resistance tests before the magnetising current measurement is carried out. The residual flux could impact the measurement.
1.4 Capacitance & Dielectric Dissipation (Power) Factor
  1. Capacitance: Winding to winding: change of the geometry between windings due to high currents or mechanical damage.
  2. Winding to ground: change of the geometry between winding and ground due to high currents or mechanical damage.
  3. Core to ground: change of the core position to the tank due to mechanical damage
  4. Condenser bushings: breakdowns between grading layers
  5. Dielectric Dissipation Factor or Power Factor: Insulation failures, contamination of insulation liquids with particles, acids, water in solid and liquid insulation, partial discharges due to bad contacts on bushing test tap, breakdown in bushing condenser layers.
Indication: Moisture, tests on regular bases (e.g. on high voltage bushings).
Test Method: A sinusoidal HV AC source (preferable with variable frequency) is connected to the test object in parallel to a low loss reference capacitor.
The currents through the test object and through the reference capacitor are measured and the time difference between their zero crossings is determined. The loss angle delta can be calculated from this time difference. Normally this test is done at 10 kV for on-site measurements.
The following figure shows the equivalent parallel circuit of an insulator (capacitance) with its losses (resistance) and the comparative definitions of Dissipation Factor (DF) and Power Factor (PF), expressed as a ratio of currents in the equivalent circuit components.
For historical reasons, European countries mostly use DF, whereas PF is mostly used in North America. For values up to 10%, the typical range for insulating material, DF and PF are numerically equivalent anyway.
Figure 1 – Insulation equivalent circuit and Definitions for DF and PF
This test method, and its result, may be referred to by many terms such as loss factor, loss angle, dielectric loss angle (DLA), tan δ, tangent delta, δ, dielectric dissipation factor (DDF), dissipation factor (DF), power factor (PF), Cos φ or Cos θ.
The units of measure can also vary: radians, milli-radians (mR), %, 0/00 (rarely used). The absence of units usually means the result is the arithmetic value of cos φ or tan δ.
Reference: Test report, fingerprint measurements, trend analysis, comparison to identical units Nameplate values for bushings.
Interpretation: For measurements on windings, values are normally in the order of 0.5%. A measurement higher than 1% is questionable. For bushings, the following values are given in IEC and IEEE standards:
Table 1 – DF and PF values for bushings according to IEC 60137 and IEEE C.57.19.01
TypeRIPOIPRBP
InsulationResin impregnated paperOil impregnated paperResin bonded paper
DF tan δ (RT)
by IEC 60137
< 0,7%< 0,7%< 1,5%
PF cos φ (RT)
by IEEE C.57.19.01
< 0,85%< 0,5%< 2%
Typical new values0,3-0,4%0,2-0,4%0,5-0,6%
Note that all values are measured at 50/60 Hz and 20°C.
Comments and Suggestions: This is the most common technique for assessing the bushing condition (more information below).
Suggested Reading – Power Transformer Capacitance and Dissipation Factor Test
1.4.1 Additional Information for Bushing Diagnostics
The most common technique for assessing the condition of a bushing is the dissipation factor (DF) / power factor (PF) and capacitance measurement. Test results are then compared to nameplate values or previous tests. Increases or decreases from reference values are usually an indication of contamination and/or deterioration of the insulation system.
Limits for the maximum permissible change tend to be manufacturer and type-specific. A doubling of the initial dissipation / power factor value warrants either more frequent monitoring or replacement. A 10 % change in capacitance also warrants replacement.
The temperature of the insulation can affect the dissipation / power factor results. Temperature correction factors for OIP and RIP bushings are shown below in Figure 2. The temperature of the bushing lies between the oil temperature of the transformer and the ambient temperature. The temperature of the oil and the ambient temperature should be recorded in the test report.
Figure 2 – Effect of Temperature on Dissipation / Power Factor (tanδ) Measurement
Leakage currents across the surface of the outer insulator (porcelain or silicone) may also have some influence, particularly if the surface is dirty and wet. In case of unexpectedly high dissipation / power factor values, the bushing should be cleaned before the measurement is repeated. For silicone composite bushings, the cleaning instructions of the manufacturer should be followed, because some cleaning chemicals can damage the silicone.
Additionally, a collar which is connected to the guard circuit can be used to suppress the influence of the surface current. With a “hot-collar”, the capacitance and dissipation / power factor of the insulation between the collar and the grounded centre conductor can be measured.
This technique can be used to detect local faults in bushings or low oil level in oil-filled bushings.
All given reference values are valid for the capacitance “C1”, which lies between the inner conductor and the measuring tap. In oil-filled bushings, the dielectric losses of the capacitance “C2”, which lies between the measuring tap and the flange, can give some information about the oil around the active part of the bushing.
Care has to be taken that the measuring tap is clean and dry, otherwise, this will affect the result. The evaluation is based on a comparison of tests on similar bushings on the transformer. The condition of bushings can also be evaluated using infrared thermography and, in the case of oil-filled bushings, by dissolved gas analysis of bushing oil or by monitoring the pressure within the bushing.
The bushings are sealed and leak tested at the time of manufacturing. In order to take an oil sample, the bushing has to be opened and this introduces a risk of improper re-sealing and possible contamination (moisture, dust) after sampling is completed. It is therefore recommended not to sample oil on bushings.
However, when a problem is known, for example, high dissipation/power factor for the C1 measurement, there might be a need for oil sampling and gas analysis. The interpretation of the analysis is done according to IEC 61464. If questions remain, the manufacturer can usually assist with the evaluation.
If oil needs to be sampled the following recommendations should be followed:
  1. Ask the original manufacturer for a sampling procedure.
  2. The sample is preferably taken during dry weather conditions.
  3. If this is not possible, clean the area around the sampling plug, and also protect that area from rain.
  4. The internal pressure of the bushing must not be altered before and after the sampling. This requirement is satisfied if the sample is taken when the mean temperature of the bushing is between 0°C and 30°C.
  5. The time when the bushing is open should be as short as possible.
  6. Immediately replace the removed oil with an equal amount of new, dry, degassed transformer oil.
  7. The gasket should always be replaced when the bushing is re-sealed.
Because bushings are hermetically sealed components, measuring the pressure of the oil within the oil-filled bushing is a valuable diagnostic tool. The advantage is that it allows monitoring of the online condition of the bushing to detect possible oil leakage or overheating.
However, this requires the bushing to be installed already equipped with a pressure sensor at the foot of the bushing.
Suggested Video – Diagnosing HV Bushings by OMICRON
1.5 Leakage Reactance (Short-Circuit Impedance)
Detectable Failures: Deformation of windings.
Indication: High through current faults, high inrush currents, Buchholz relay tripping, protective relay tripping.
Test Method: An AC source (preferable with variable frequency) is connected to each phase of the HV winding with the corresponding LV winding short-circuited. The source current and the voltage across the HV winding are measured to determine the leakage impedance.
To determine the leakage reactance, the imaginary part of the complex impedance has to be measured. This can be done by using a complex impedance measuring device or a wattmeter to determine the real part of the complex impedance. The reactance can be calculated from these results.
Reference: Fingerprint measurements (one phase test), or comparison to identical units.
Interpretation: The measured impedance should not differ more than 2% compared to the factory test report.
The difference between phases is usually less than 2%. Changes >1% ought to be investigated with other tests such as FRA. Care is required comparing 3 phase and 1 phase test measurements.
Comments and Suggestions: The test can be done also from the LV side, but in this case, the values have to be corrected using the square of the winding ratio.
Suggested Reading – Load flow and short circuit analysis of a MV substation (case study 33/11 kV substation in ETAP)
1.6 Insulation Resistance
Detectable Failures: Insulation deterioration or failures in the windings or core earthing.
Indication: Buchholz relay tripping, DGA.
Test Method: A high DC voltage (typical values are 1kV up to 5kV) is applied to the winding under test. The insulation between the core and tank can also be verified by this measurement. The leakage current is measured and the insulation resistance calculated and indicated by the instrument.
As this measurement uses DC voltage, the measurement cannot be compared with AC losses that comprise of polarisation losses and capacitive coupling through the insulation. The temperature can affect the measurement results. The test voltage and temperature must be recorded.
Reference: Test report, fingerprint measurements, comparison to identical units.
Interpretation:
  • Transformers with rated voltage > 69kV, >1GΩ measured at 20°C
  • Transformers with rated voltage ≤ 69kV, >500MΩ measured at 20°C
Another way of applying Insulation Resistance is to measure the Polarization Index (PI) by measuring the current after 1 and 10 minutes of voltage application. The PI was introduced to detect moisture in the winding insulation of rotating machines. For the complex oil-cellulose insulation system of transformers, the PI results can be misinterpreted. FDS/PDC measurements are preferred for quantitative assessments of the moisture in the insulation.
The measurement of the insulation resistance can influence RVM, PDC and FDS measurements if they immediately follow the Insulation Resistance test.
Suggested Video – Insulation Resistance (IR) test of 3-phase distribution transformer
1.7 Core Grounding
Detectable Failures: Multiple core grounding by core grounding faults.
Test Method: The test can be done only if the core grounding can be disconnected outside the tank to measure the insulation resistance of the core to the ground.
Interpretation: The insulation resistance of the core to the ground is in the order of 10MΩ or higher. Values lower than 100kΩ can indicate core grounding problems. In some cases, resistances are used to ground separated core lamination packets. These resistances are normally in the order of several kΩ.
Comments and Suggestions: Measurements of the core ground current in service, show that the measured current is in the order of some mA for a well-insulated core. If the core has grounding faults, the current is several amps or even higher.
Suggested Reading – The mystery of nuisance tripping incidents in transformer protection
The mystery of nuisance tripping incidents in transformer protection that worry engineers
2.1 Frequency Response Analysis (FRA)
Detectable Failures: Shorted turns, core faults, winding deformation, winding displacement, faulty core grounding, faulty screen connections, damage during transportation.
Indication: High through fault currents, Buchholz relay warning or tripping, DGA, impact recorder results (transportation).
Test Method: Frequency Response Analysis (FRA) is a method to evaluate the mechanical and geometrical integrity of the core and windings within a power transformer by measuring the electrical transfer functions over a wide frequency range. The FRA is a comparative method, that evaluates the transformer condition by comparing the obtained set of FRA results to reference results on the same, or a similar, unit.
Method 1 – Sweep Frequency Response Analysis SFRA: A sinusoidal AC voltage with variable frequency (several Hz to several MHz) is connected to each phase of the HV and the LV windings with all other windings open-circuited.
The input voltage (Uin) and the output voltage (Uout) are measured at different frequencies. For both Method 1 and Method 2, the ratio “20 log (Uout / Uin)” (in dB) is calculated for each frequency and the results are plotted on a trace.
Method 2 – Impulse Frequency Response Analysis IFRA: An impulse is injected into each phase of the HV and the LV windings with all other windings open-circuited. The input and output impulse curves = f(t) of the windings are recorded. The time-domain results are transformed into the frequency domain by using FFT algorithms. The input voltage (Uin) and the output voltage (Uout) are calculated for different frequencies.
It is observed that both methods give satisfactory results but Method 2 does not give results in the low-frequency range (below 1kHz).
Reference: Three methods are commonly used to assess the measurements (traces):
  1. Time-based (current FRA results will be compared to previous results of the same unit)
  2. Type-based (FRA of one transformer will be compared to an equivalent type)
  3. Phase comparison (FRA results of one phase will be compared to the results of the other phases of the same transformer)
Interpretation: No limits are defined. Comparison with benchmark data will indicate changes.
Comments and Suggestions: For transportation assessment the FRA should be the last test before departure and the first test upon arrival. No winding resistance DC measurement should be made before an FRA measurement is carried out. The residual flux could impact the measurement.
Benchmark raw data should be stored to facilitate later comparisons.
Suggested Video – Frequency Response Analysis with OMICRON FRAnalyzer
2.2 Polarization/Depolarization Current (PDC) Method Detectable failures
Detectable Failures: Water content in the solid cellulose insulation of oil-paper insulation, insulation failures, ageing of insulation, contamination of insulation liquids with particles, acids, water in solid and liquid insulation, partial breakdowns of capacitive bushing layers.
Indication: High moisture in the oil, general assessment of insulation condition.
Test Method: The principle of this measurement is to apply a DC voltage across the insulation during a certain time and to measure the polarisation current. Then the insulation is short-circuited at a variable time and the current is measured again (depolarisation current).
Dielectric diagnostic methods deduce moisture in paper or pressboard from the polarization and depolarization currents measured at time intervals. Experience shows that moisture strongly influences these measurements. The dielectric response of insulation can be recorded in the time domain or the frequency domain.
A time-domain current measurement records the charging and discharging currents of the insulation. The derived measurement method is called the Polarization Depolarization Current method.
Figure 3 – Polarisation and Depolarisation Current
Reference: Moisture determination by modelling, comparison to fingerprint measurements
Interpretation: Moisture determination is based on a comparison of the transformer’s dielectric response to a modelled dielectric response. An algorithm rearranges the modelled dielectric response and delivers moisture content and oil conductivity.
A reliable moisture analysis of on-site measurements is based on an exact data pool for the modelled dielectric response. The data pool includes the measurements on the new pressboard at various temperatures, moisture contents and oils used for impregnation. Once water content has been assessed, refer to the limits for dry, moderately wet and extremely wet insulation provided in IEC 60422.
Comments and Suggestions: New procedures consider also the dielectric properties of aged pressboard in order to compensate for the influence of ageing.
Suggested Video – Polarization index testing theory
2.3 Frequency Domain Spectroscopy (FDS)
Detectable Failures: Water content in the solid cellulose insulation of oil-paper insulation, insulation failures, contamination of insulation liquids with particles, acids.
Test Method: The principle of this measurement is the same as Capacitance and Dissipation / Power Factor described previously but differs by being applied at different frequencies, typically from 0.001 Hz to 1000 Hz as shown in the following traces:
Figure 4 – Frequency Domain Spectroscopy
Reference: Moisture determination by modelling, comparison to fingerprint measurements, limits for dry, moderately wet and extremely wet insulation are given in IEC 60422.
A reliable moisture analysis of the on-site measurements is based on matching them with a data pool for the modelled dielectric response. The data pool consists of measurements on the new pressboard at various temperatures, moisture contents and oils used for impregnation. New procedures consider also the dielectric properties of aged pressboard as well in order to compensate for the influence of ageing. Once water content has been assessed, refer to the limits for dry, moderately wet and extremely wet insulation provided in IEC 60422.
Comments and Suggestions: The combination of time-domain polarization current measurements with frequency-domain spectroscopy reduces the test duration compared to existing techniques.
Essentially, time-domain measurements can be accomplished in a short time but are limited to low frequencies (typically below 1 Hz). In contrast, frequency-domain measurements are feasible for high frequencies as well but take a very long time at low frequencies.
In its application to high voltage bushings, the measurement of Dissipation / Power Factor at low frequencies (some Hz) enables the detection of moisture with high sensitivity. Figure 16 below demonstrates the typical moisture sensitivity of the Dissipation / Power Factor Measurement on OIP bushings between 20 Hz and 400 Hz.
Figure 5 – Dissipation / Power Factor Measurement on OIP Bushings at Different Frequencies
As a guide, indicative limits for Dissipation / Power Factor in new and aged bushings at frequencies of 15 Hz, 50/60 Hz and 400 Hz are given in the following table.
Table 2 – Indicative DF/PF Limit Values for Condenser Bushings
RIP
Resin impregnated
OIP
Oil impregnated
RBP
Resin bonded paper
Frequency*newagednewagednewaged
15 Hz<0.6%<0.7%<0.5%<0.7%<0.7%<1.5%
50/60 Hz<0.5%<0.5%<0.4%<0.5%<0.6%<1%
400 Hz<0.6%<0.7%<0.5%<0.7%<0.7%<1.5%
* at 20°C
2.4 Electrical Method for Partial Discharge (PD) Measurement
Detectable Failures: Partial discharges, singular insulation faults.
Indication: DGA
Test Method: For detection, different types of coupling are used, for example, bushing capacitance taps, high-frequency current transformers or coupling capacitors.
The test method outlined in IEC 60270 is a useful tool because it is a sensitive method and can be calibrated. Electromagnetic noise external to the transformer can interfere with the measurement. For this reason, the method may be unsuitable for some on-site measurements.
However, modern multi-channel PD measuring systems which can record the PD on all channels simultaneously, and new methods such as the Three-Phase Amplitude Relation Diagram (3PARD) or the Three-Centre Frequency Relation Diagram (3CFRD), can be used to separate PD sources from each other and from external electromagnetic noise (interference).
Reference: Fingerprint measurements, trend analysis.
Interpretation: For PD On-site measurement, limits cannot be defined; This technique can be used with Acoustic PD in order to facilitate PD localization.
Comments and Suggestions: PD measurement is important to detect and locate a weakness in the insulation system. Partial discharge activity typically occurs within insulation voids, on ungrounded metal objects lying in an electric field, or as corona due to the intense electric stress on the insulation surrounding sharp-edged/shaped electrodes.
In transformers, some PD sources include gas bubbles in the oil, voids in solid insulation material or floating metallic particles. The long term effect of PD is destructive for organic insulation systems, by degrading their insulation qualities.
A significant increase of the PD level or the rate of the PD can provide an early indication for evolving defects. The PD pulses generate electromagnetic waves, acoustic signals, chemical reactions, local heating and optical signals.
Different techniques can be used to detect these phenomena.
Suggested Video – Partial Discharging (PD) testing an iron-core tuning reactor at NEPSI
2.5 Acoustic Partial Discharge (PD) Measurement
Detectable Failures: Partial discharges.
Indication: DGA
Test Method: The acoustic partial discharge measurement uses the fact that an acoustic signal is emitted by PD activity as a result of pressure fluctuations. Because of the short duration of the PD impulses, the resulting compression waves have frequencies that range up to ultrasonic. The frequency spectrum lies in the range between several Hz and several 100 kHz.
In transformers, mechanical waves generated by PD propagate through the oil, hitting the tank walls where Piezoelectric sensors for acoustic signal detection are fixed externally. By using trigonometry techniques, the source of the acoustic emission can be localized, greatly assisting any corrective maintenance.
This method has limited sensitivity to PD faults on the inner windings. It is also very sensitive to noise which is not generated by the internal PD. To improve the sensitivity, this method can be combined with the electrical PD method or with the UHF PD method. The electrical signals can be used to trigger the recording of acoustic signals. By using an averaging algorithm, the influence of the acoustic noise coming from other sources outside the tank can be reduced.
Interpretation: For Acoustic PD measurements, there are no limits applicable.
Suggested Video – Power Transformer Partial discharge testing & global monitoring solutions
2.6 Partial Discharge (PD) Measurement using UHF Technology
Detectable Failures: Partial discharges, Singular insulation faults.
Indication: DGA
Test Method: Decoupling of the UHF PD signals from within the tank of a power transformer requires the sensitive UHF sensors to penetrate through the tank wall. Alternatively, a UHF antenna installed inside the tank is used. UHF signals have much less damping than acoustic signals.
Because of the sensitivity differences between UHF and acoustic signals, it can be advantageous to combine the two methods. By averaging the acoustic signals, by triggering them with the high sensitivity to arriving UHF impulses, the influence of acoustic noise can be reduced.
The important localization of the PD is achieved by using the acoustic signal travel times. Wave shape and time of flight methods may be used for the localisation of PD sources.
Interpretation: For UHF PD measurements, there are no limits applicable.
Suggested Video – Demonstration of UHF partial discharge location in a power transformer using time-of-flight techniques.
2.7 Frequency Response of the Stray Losses (FRSL)
Detectable Failures: Local overheating due to excessive eddy current losses linked by the stray flux. Short circuits between parallel strands of Continuously Transposed Conductors (CTC).
Indication: If parallel strands of CTC have short circuits between them, the losses in the stray channel are increased. This results in high internal temperatures, normally indicated by the DGA.
Test Method: An AC source with variable frequency (typically some Hz up to some hundred Hz) is connected to each phase of the HV winding with the corresponding LV winding short-circuited. The source current and the voltage across the HV winding are measured. The stray losses are represented by the AC resistance of the short circuit impedance at higher frequencies. The resistive part of the complex impedance has to be measured.
This can be done by using a complex impedance measuring device. Instead of the complex impedance measuring device, a wattmeter can be used to determine the real part of the complex impedance.
Reference: Comparison of the three phases, fingerprint measurements (one phase test)
Interpretation: ∆L: Less than 2.5% between phases; ∆R: Less than 15% between phases.
Comments and Suggestions: The test can be done also from the LV side. For comparison of the results the values have to be corrected by the square of the winding ratio.
Suggested Video – Three-phase test system for comprehensive power transformer testing
2.8 Recovery Voltage Method (RVM)
Detectable Failures: Trend indication of internal moisture or ageing in oil-paper insulation.
Indication: High moisture in the oil.
Test Method: DC voltage measurements are used to record a recovery voltage that develops across composite oil-solid insulation due to the phenomenon of space charge relaxation. Initially, the insulation is charged with a DC voltage over a certain time. Next, a short circuit is applied for a much shorter time (typically half the charging time). The short circuit is then removed and the recovery voltage is measured, with its maximum value used for the assessment.
This is one of a series of recovery voltage measurements taken with steadily increasing charging times. The accumulated series of voltage maxima yields a “Polarization Spectrum” used to evaluate the moisture content in cellulose. This derived diagnostic is the Recovery Voltage Method (RVM).
Interpretation: The RVM (Return Voltage Measurement) in its present form can only be used for trend indication.
Suggested Video – Dielectric Response Analysis – Basics
3. Summary Table
Table 3 – Summary of the typical problems that may be detected with electrical tests and dissolved gas analyses (DGA)
Test TypeDiagnostic TechniqueType of problem
Winding Turn to Turn InsulationWinding, Bushing InsulationWinding, Bushing, OLTC ContinuityWinding GeometryMagnetic Circuit InsulationMagnetic Circuit Integrity
Basic
Tests
Winding Ratio
Winding Resistance
Magnetisation current
Capacitance and DF/PF
Leakage Reactance
Core Ground Test
Special
Tests
Frequency Response of Stray Losses
Polarisation/Depolarisation
Electrical Detection of PD
Acoustical Detection of PD
UHF Detection of PD
Dissolved Gas Analysis (DGA)
Reference: Guide for Transformer Maintenance: C. Rajotte ( CA) – (Convener), TF Leaders: M. Foata (CA), P. Jarman (UK), F. Larese (FR), P. Lorin (CH), B. Pahlavanpour (UK), J.P. Patelli (FR), J. Velek (CZ), R. Willoughby (AU), R. Barrento (PT), P. Boman (US), I. Diaconu (RO), A. Drobyshevski (RU), Y. Ebisawa (JP), T. Fagarasan (RO), N. Fantana (DE), H. Gago (ES), J. Gebauer (DE), P. Gervais (CA), M. Krüger (AT), G. Lawler (IR), R. Maina (IT), C. Moldoveanu (RO), P. Mueller (CH), D. Olan (CA), L Paulhiac (FR), M. Pena (BR), E. Perez-Moreno (ES), S. Quintin (ES),V. Samoilis (GR), F. Simon (FR), A. Shkolnik (IS), B. Sparling (CA), and P. Warczynski (PL).
  1. Babiker Ahmed
    May 08, 2022
    Very much interested. Need further clarification or discussion.
    B Ahmed
    Electrical Engineer
  2. sanjeev pareek
    Oct 18, 2021
    It’s a superb article. Complete and very useful. All practical aspects covered in detail.
  3. David L. Bowles
    Sep 14, 2021
    Wonderful presentation! I find it complete and accurate. I look forward to viewing more articles like this one in the future.
Leave a Reply to sanjeev pareek