Home / Technical Articles / Protecting Oil Type Transformer with Buchholz Relay
Introduction to Buchholz Relay
Buchholz relay is a gas-actuated relay installed in oil immersed transformers for protection against all kinds of faults. Named afteri ts inventor mr. Max Buchholz (1875–1956) in 1921, relay is used to produce an alarm in case of incipient (i.e.slow-developing) faults in the transformer and to disconnect the transformer from the supply in the event of severe internal faults.
It is usually installed in the pipe connecting the conservator to the main tank. It is a universal practice to use Buchholz relays on all such oil immersed transformers having ratings in excess of 750 kVA. The Buchholz relay is a protective rely for equipment immersed in oil for insulating and cooling purpose.
It is intended mainly for transformers or choke coils having a conservator vessel.
The relay responds to the accumulation of gas or air inside the apparatus when the oil level is too low or the flow of oil unusually strong. The relay neither gives a warning signal or disconnects the endangered equipment.
The Buchholz relay operates even on very slight faults which are just in process of developing, so that greater damage may be prevented.
Protection Range
The relay is particularly effective in case of:
  1. Falling oil level owing to leaks
  2. Short circuited core laminations
  3. Short – circuits between phases
  4. Broken-down core bolt insulation
  5. Earth faults
  6. Bad contacts
  7. Puncture of bushing insulators inside tank
  8. Overheating of some part of the windings
In the event of a fault, oil or insulations decomposes by heat, producing gas or developing an impulse oil flow. To detect these phenomena, a Buchholz relay is installed.
The Buchholz relay is installed at the middle of the connection pipe between the transformer oil tank and the conservator, so that, upon a fault development inside a oil transformer, an alarm is set off or the transformer is disconnected from the circuit.
Construction and technical characteristics
Buchholz relay contruction
PositionDescription
1-2Release terminals
3-4Alarm terminals
5Earth terminal
6Breather cock
7Valve of pneumatic test
8Mechanical test of the alarm/release circuit
9Cable gland
10Drain plug
Casing Non porous weatherproof compact casting of light aluminium alloy painted.
Cover Non porous weatherproof compact casting of light aluminium alloy painted. On the cover are located : the terminal box, the valve of pneumatic test, the breather cock, the button for mechanical test of alarm and trip circuits.
Inspection windows Special tempered glass with graduated scale in cm3.
Contacts – They can be mercury switches or magnetic actuated switches (reed contacts). On request it’s possible to supply change-over switches.
Switches characteristics
Rated voltage:
24 ÷ 250V AC or DC
Rated current: 0,5 A (10000 tests)
Breaking capacity: 2 A AC (cos = 0,4 ÷ 25% – 50Hz) 2A DC (T = L / R = 40 msec).
Mechanical protection degree IP 54
Insulation 2000V 50Hz between terminals and earth for a 60 seconds time.
Working temperature Oil temperature range: – 25 / +115°C.
Vibration test (in normal operative conditions)
Oscillation amplitude: 2mm
Time diagram:
0Hz ÷ 100Hz 30 sec.
100Hz (200 vibrations/sec.) 60 sec.
100Hz ÷ 0Hz. 30 sec.
Contacts capacity to withstand vibrations
Mercury sw: 150 horizontal vibrations/sec. (75Hz) first signals of closing contacts 120 vertical vibrations/sec. (75Hz) first signals of closing contacts.
Magnetic sw: 200 horizontal vibrations/sec. (100Hz) no one signal of closing contacts 200 vertical vibrations/sec. (100Hz) no one signal of closing contacts.
Function of Buchholz relay
In the following the operation of a Buchholz relay is explained using the example of a double-float  Buchholz relay. The relay is built in the connecting pipe between the transformer tank and the  conservator. During normal operation it is filled completely with insulating liquid.
Due to buoyancy the  floats are at their top position. If a fault occurs inside the transformer, the Buchholz relay responds as  follows:
Gas accumulation
Gas accumulation in Buchholz relay
Fault: Free gas is available in the insulating  liquid.
Response: The gas in the liquid moves upwards, accumulates in the Buchholz relay and displaces the insulating liquid level. The moving float actuates a switch contact (magnet contact tube). An alarm signal is tripped. The lower float is not affected as from a certain gas volume the gas flows through a piping to the conservator.
Insulating liquid loss
Insulating liquid loss in Buchholz relay
Fault: Insulating liquid loss due to leakage.
Response: As the liquid level falls the top float moves downward. An alarm is tripped. If the liquid loss continues, conservator and piping as well as the Buchholz relay will be emptied. As the liquid level falls, the lower float moves downward. The moving float actuates a switch contact so that the transformer is disconnected.
Insulating liquid flow
Fault: A spontaneous incident generates a pressure wave moving in the direction of the conservator.
Response: The liquid flow reaches a damper arranged in the liquid flow. If the flow rate exceeds the operating threshold of the damper, the latter moves in flow direction. Due to this movement a switch contact is actuated so that the transformer is disconnected.
Insulating liquid flow - Buchholz relay
Insulating liquid flow – Buchholz relay
The upper and lower switching system form a functional unit in the single-float Buchholz relay. In case of a fault, the single-float Buchholz relay normally isolates the transformer immediately from the mains system.
Wiring Diagrams
Standard Wiring Diagram
Buchholz relay - Standard wiring diagram
Buchholz relay – Standard wiring diagram
Mounting Sketch
Buchholz relay - Mounting sketch
Buchholz relay – Mounting sketch
Advantage
1. It is the simplest form of transformer protection.
2.It detects the incipient faults at a stage much earlier than is possible withother forms of protection.
Disadvantage
1. It can only be used with oil immersed transformers equipped withconservator tanks.
2. The device can detect only faults below oil level in the transformer. Therefore, separate protection is needed for connecting cables.
References:
  1. Terman – Buchholz relay broshure
  2. EMB Elektromotoren und Gerätebau Barleben GmbH – Transformer Protection Relays (Buchholz Principle)
20 Comments
  1. BIRAJ BARUUAH
    Nov 30, 2021
    how on puncher of insulation core ,this bucholz will work?
  2. Omar Eyad Aljorani
    Jun 16, 2021
    What happens if the buchholz relay is connected in the opposite direction?
  3. satyadeo vyas
    Jan 15, 2021
    Explained beautifully
  4. Ravi
    Nov 21, 2020
    Didn’t mention that what type of gases generated in transformer during faults and which kind of gas operates buchoz relay.
  5. Alozie Nathan Onyedikachhi
    Apr 11, 2020
    Very Nice and well explained
  6. MOHAMED ALGELANY
    Apr 11, 2020
    good article easy to understand working of relay & how it protects the transformer . thank you very much Sir
  7. visanu ponluksanapimol
    Apr 11, 2020
    Thank you for inform and I follow up knowledge of electrical engineering from your site
  8. Shakeel Haider test inspector iesco Pakistan
    Apr 11, 2020
    There are some problems in HV / lv bushing, or in HV Winding, / lv Winding, resion for gas development in main tank of t/f,
  9. lawrence jaricha
    Sep 01, 2019
    very insightful im frm zimbabwe
  10. Sanjay Bhalodiya
    Apr 25, 2019
    Dear All,
    Have you anyone has faced problem of Buchholz relay maloperation ?
    It seems due to one of its internal connection (normally open contact connection) out of 3 get earthed & showing zero IR value.
    Relay is MR/CEDASPE make
    Regards,
    Sanjay
  11. brian cantwell
    Oct 27, 2017
    one sentence is incorrect The relay neither (should be either) gives a warning signal or disconnects the endangered equipment.
    • alao adeola
      Dec 18, 2017
      Brilliant.
    • Cyrix
      Aug 29, 2018
      Very right !!!
  12. Hemandra S Bisht
    Dec 19, 2015
    Dear All ,
    I am facing frequent gas accumulation in one of my 56.25 MVA Transformer 13KV/11 Voltage Level of Schneider Make.
    Transformer is Charged from 132 KV Side & present condition is no Load (Running Load is approximate 150 KV . Gas is accumulated in bucholz after every 24 hrs , I am not able to find the reason. Pl help me in findout reson of this problem
  13. prakash
    Jan 11, 2015
    very good article easy to understand working of buchholz relay & how it protects the transformer . thank you
  14. singaraj
    May 16, 2014
    dear team,
    super it’s very nice & easily understand
  15. mrjaykumartrivedi
    May 06, 2014
    Nice and easy concepts about protection of power transformer. I also written my own think about protection of transformer. You can read it and just tell me how it is ? http://electricallife.com/transformer-protection/
  16. Magnito
    Nov 09, 2012
    Very helpful & well written article on all you need to know about the Buchholz relay.Thanks EEP
    • Hugodp
      Oct 25, 2013
      Hi
      Is it possible to damage the floats and switching mechanisms when injecting gas into a buchholz relay through the petcock.
Leave a Reply to Shakeel Haider test inspector iesco Pakistan
80  −  77  =
