Home / Technical Articles / Shaping and connecting rigid busbars in low voltage switchgear
Busbars – machining, bending and shaping
The busbars constitute the real “backbone” of every low voltage switchgear. The main busbar and branch busbars supply and distribute the energy. Creating busbars generally involves machining, bending and shaping which require a high degree of expertise to avoid weakening the bars or creating stray stresses.
Shaping and connecting rigid busbars in LV switchgear
Shaping and connecting rigid busbars in LV switchgear (photo credit: Edvard Csanyi)
The same applies to connections between bars, whose quality depends on the sizes and conditions of the contact areas, and the pressure of this contact (number of screws and effectiveness of tightening).
  1. Sizes of the contact areas
  2. Contact pressure
  3. Condition of the contact areas
  4. Machining copper busbars
  5. Bending bars
The contact area (sc) must be at least 5 times the cross-section of the bar (Sb). Sc > 5 × Sb for main busbar continuity links, it is advisable to establish contacts along the entire length of the bar in order to ensure optimum heat transfer.
Busbar contact area and cross-section
Figure 1 – Busbar contact area and cross-section
For branch busbars, the contact area can be smaller, complying with the condition Sc > 5 × Sb. For equipment connection plates, contact must be made over the whole surface of the plate for use at nominal current.
Busbars contact area
Figure 2 – Busbars contact area
Connection aplate surface
Figure 3 – Connection aplate surface
TIP! Connection on extension rod, adaptor or spreader:
Figure 4 – Connection on extension rod, adaptor or spreader
Go back to creating busbars actions ↑
2. Contact Pressure
The contact pressure between bars is provided using screws whose size, quality, number and tightening torque are selected according to the current and the sizes of the bars.
Too high a tightening torque or not enough screws can lead to distortions which reduce the contact area!! It is therefore advisable to distribute the pressure by increasing the number of tightening points and using wide washers or back-plates.
Busbars contact pressure
Figure 5 – Busbars contact pressure
Devices to prevent loosening:
Figure 6 – Devices to prevent loosening
Applying a mark (paint, brittle coating) will show any loosening and can also be used to check that tightening has been carried out correctly (tell-tale)
Figure 7 – Applying a mark (paint, brittle coating)
Left: Connection on 120 x 10 bars (4000 A); Right: Double connection: 100 x 10 bars (3200 A) and 80 x 10 bars (2500 A) on common 120 x 10 bars
Figure 8 – Left: Connection on 120 x 10 bars (4000 A); Right: Double connection: 100 x 10 bars (3200 A) and 80 x 10 bars (2500 A) on common 120 x 10 bars
Recommended screws and minimum characteristics
I [A]Bar width
[mm]
Number
of screws
∅ Screw
[mm]
Minimum
quantity
Tightening
torque
[Nm]
1 bar2+ bars
≤ 250≤ 251M88-815/20
2M68-810/15
≤ 400≤ 321M106-830/35
≤ 630≤ 501M126-850/60
2M106-830/35
2M88-815/20
8001250≤ 804M88-815/20
4M106-830/35
10001600≤ 1004M106-830/35
2M126-850/60
16002500≤ 1254M126-8 50/60
Tightening torques that are too high lead to the limit of elasticity of the bolts being exceeded and creeping of the copper.
Apart from pronounced oxidation (significant blackening or presence of copper carbonate or “verdigris”), bars do not require any special preparation.
Cleaning with acidified water is prohibited, as, apart from the risks, it requires neutralisation and rinsing. Surface sandin (240/400 grain) can be carried out, complying with the direction of sanding so that the “scratches” on bars that are in contact are perpendicular.
Busbars contact area condition
Figure 9 – Busbars contact area condition
4. Machining copper bars
Copper is a soft, “greasy” or “sticky” metal in terms used in the trade. shaping is generally carried out dry, but lubrication is necessary for high-speed cutting or drilling operations (up to 50 m/mn).
Sawing (8D medium tooth) in a clamping vice
Figure 10 – Sawing (8D medium tooth) in a clamping vice
It is possible to make holes with drills for steel, but it is preferable to use special drills (with elongated flutes for easy detachment of chips)
Figure 11 – It is possible to make holes with drills for steel, but it is preferable to use special drills (with elongated flutes for easy detachment of chips)
The hydraulic punch is used to make precision holes easily … and with no chips.
5. Bending busbars
It is strongly recommended that a full-scale drawing is made of the bars, in particular for bends and stacking of bars.
Bending busbars
Figure 12 – Bending busbars
The bars are separated by their thickness “e”. The total centre line length before bending is the sum of the straight parts (L1 + L2) that are not subject to any distortion and the length of the curved elements on the neutral line (in theory at the centre of the thickness of the metal).
Bending to 90°
l = (2πR) / 4 = (2r + e) × π / 4
Useful formula: l = R × 1.57
Bending busbars to 90°
Figure 13 – Bending busbars to 90°
Bending to any angle α
l = (2r + e) × π × (180 – α) / 360
  • r is bending radius (or radius of the tool)
  • R is radius to the neutral line R = r + e/2
  • l is length to the neutral line
Figure 14 – Bending to any angle α
Creating a twist
The length L of the twist is at least twice the width l of the bar:
Creating a twist
Figure 15 – Creating a twist
Calculation note!
The calculation must be carried out based on the tool used and its actual bending radius r.
Bending on bending machine: r = 1 to 2e
Figure 16 – Bending on bending machine: r = 1 to 2e
Bending on V-block: r min. = e
Figure 17 – Bending on V-block: r min. = e
Reference // Busbars and distribution by Legrand
12 Comments
  1. Yi Chun
    May 31, 2025
    Hi, in this article “https://electrical-engineering-portal.com/shaping-connecting-rigid-busbars”, what does the pressures 1bar and 2+bars referring to, in the table for “Recommended screws and minimum characteristics”, please?
  2. khalid Naeim
    Nov 04, 2024
    Please I need calculation for numbers of cooling fans for power transformers. (ONAF)
  3. Martin Enrique Martiínez Salgad
    Nov 03, 2024
    Dear Sirs
    I would like to inform you taht I have a premium accounto with EEP but every time that a new Technical guide, article, studio or paper comes to my computer I can not access directly to it .
    every time I have to go ito your systens with my Email and password an then when I want to return to paper, technical guide, article or technicalstudio that you have sent to me the systems don not permit to access and I have to look for in all you webpage
    Before, in the beggining when my subscriptions beggins, I had not that problem, all was very easy. I think the access should be easier ad quicker .
    Thanks in advance for your help
  4. Saidur
    Nov 04, 2023
    Thank you for posting this article!
  5. Mr. Vo
    Jun 03, 2020
    Dear Sirs.
    Above information (Sb>5*Sc….) that what standard belongs to? (Example: IEC?, JIS?, NFC?…)
    • Ramesh Kapur
      Jun 13, 2022
      Vo,
      One of the standard in use is DIN 43670
  6. Jacky Lai
    Jun 21, 2019
    Ask a question ,What’s the meaning in the table “Recommended screws and minimum characteristics” of Minimum quantity 8-8、6-8?
    Can you explain it clearly? thanks
    Thanks for this sharing, it’s very useful.
  7. Mohamed
    Jun 05, 2019
    Thank you for this sharing , very interesting article
  8. Jeremy
    Dec 09, 2016
    Thank you for the information. It was very helpful
  9. David P
    Dec 07, 2016
    I would like to have use of Belleville washers addressed. Our physical plant specs require used of these washers to connect sections of switchgear together.
  10. Khakis Khan
    Dec 07, 2016
    Thanks, your article very informative and contains professional information. Which is useful for the engineers working in the field.
  11. Kondal
    Dec 06, 2016
    Thank you for the articles being posted.
    I am an electronics person working in Maintenance of UPS systems.
    Thanks once gain.
Leave a Reply to Martin Enrique Martiínez Salgad
  +  51  =  55