Home / Technical Articles / People response to short-term exposure to electric fields of AC transmission lines
How does it affect people?
Short-term exposures to electric fields produced by AC transmission lines and stations can be pretty serious and may be classified according to the type of effect causing a sensation in people. Information in this article is taken from the study that was performed by EPRI on EHV and UHV transmission lines.
Let’s discuss about three most common effects: spark discharges, electric fields and steady-state ac currents.
  1. Spark discharges, which introduce transient currents into a person when the electrical breakdown of an air gap occurs between the person’s body and a conductive object, or ground.
  2. Electric fields on the surface of the body, which exert forces on hair with consequent hair stimulation
  3. Steady-state AC currents, which enter a person contacting an object.
The preceding effects have been listed in order of practical frequency of occurrence above perception levels.
Contents:
  1. Human Response to Shocks
  2. Response to Spark Discharges
  3. Response to Steady-State Currents
  4. Response to Hair Stimulation
1. Human response to shocks
Spark discharges, causing a startle reaction or aversion to AC field exposure, are of major importance in establishing thresholds of annoyance or uncomfortable sensations. The effects of electric field on hair are of minor importance.
Responses to steady-state currents are used to establish safety limits with respect to the largest possible charged objects that a person might contact under conditions of good insulation of the object and good grounding of the person.
Such situations are infrequent and in almost all cases are preceded by spark discharges of considerable magnitude. The intensity of stimulation is classified according to the type of human response.
According to this criterion, four types of exposure may be identified:
  1. Primary shock
  2. Secondary shock
  3. Perception
  4. Below perception
Primary shocks may produce direct physiological harm. Secondary shocks cannot produce such harm but are annoying and may cause involuntary muscle reactions.
Secondary shock is of subjective interpretation, and it is difficult to define.
The IEEE PES Working Group on Field Effects (34) defines three different levels of secondary shocks:
  1. Annoyance (the person would consider the sensation to be mildly irritant if it occurs repeatedly),
  2. Startle (if it occurs unexpectedly, the sensation is likely to produce an unintentional muscular reflex that may be hazardous under a defined set of circumstances), and
  3. Aversion (the person exposed is motivated to avoid situations that he/she believes would lead to a similar experience).
Perception occurs when a person consciously detects whether or not a stimulus is present. The sensation is gentle and not necessarily unpleasant.
The preceding three categories of human response have mini-mum levels identified as:
  1. Minimum primary shock level
  2. Minimum secondary shock level
  3. Threshold of perception
Each of these levels is definable only in conjunction with a probability of occurrence in a well defined set of circumstances. This probability is expressed as a percentage of people who have reactions above a particular level.
Different practical situations that may cause discharges were investigated at Project UHV using the UHV test line to generate the induction field. A total of 136 persons, 128 men and 8 women, volunteered for these measurements, which were conducted under different weather conditions.
A number of measurement stations were prepared under the UHV test line, and people were asked to answer questionnaires about their responses to different electric field effects.
Figure 1 shows the percentage of people who experienced sensations above the threshold of perception and above the mini-mum annoyance level.
Combination of all results obtained on perception and annoyance caused by spark discharges (136 persons)
Figure 1 – Combination of all results obtained on perception and annoyance caused by spark discharges (136 persons)
The curves marked with a 4 in Figure 1 correspond to spark discharges between the thumb and the metallic shaft of an umbrella held at shoulder height. The participants were asked to hold the umbrella at the insulating handle, to move the thumb slowly until it touched the metallic shaft, and then to remove it.
UHV concurrently with the study of spark discharge sensations.
The results, presented in Figure 2 below, show the percentage of people who experienced sensations above the threshold of perception and above the minimum annoyance level.
Combination of all results obtained on perception and annoyance of hair erection and tingling (136 persons)
Figure 2 – Combination of all results obtained on perception and annoyance of hair erection and tingling (136 persons)
The curves marked with a 1 correspond to stimulation of the hair of the hand, with the subject’s arm extended over the head searching for the position where the sensation is strongest. Curve 2 corresponds to stimulation of the hair of the head (forehead, eyebrows, sideburns), with the subject’s arms at the side of the body.
Curve 3 corresponds to a tingling sensation in parts of the body covered with clothes (elbow, shoulder, sides).
The median values of thresholds of perception are presented in Table 1.
Table 1 – Median values of electric field, threshold of perception
Hand hair7 kV/m
Head hair23 kV/m
Between body and clothes20 kV/m
Median annoyance levels are much higher and are never obtained in practical conditions. The basic mechanism of hair stimulation is not fully under-stood. It is assumed that hair collects charges that give origin to a force acting on the hair, thus causing its vibrations. Hair vibrations have been observed at both 60 Hz and 120 Hz.
These observations produced different interpretations of the nature and polarity of the charges on the hair. Conductive hair, such as wet hair, has charges of the same sign as those on the skin.
Thus, the mechanical force on the hair has a frequency double that of the power frequency.
However, if the hair is insulating, a net charge of fixed polarity could remain on the hair, thus justifying a force at power frequency. The data obtained are reasonably matched by straight lines when plotted (1) with the field on a log scale and (2) with the probabilities of perception and annoyance on a normal probability scale.
The dispersion is much larger than for spark discharges, with a ratio of 7 to 9 between fields corresponding to 84% and 16% probability.
Also, for these sensations, the curves for annoyance are parallel to those for perception. The ratio between annoyance and perception fields is 6 to 10. For fields corresponding to 50% probability of perception, the probability of annoyance is 1 to 9%.
Women, probably because of less hand hair, appear to be much less sensitive to this type of electric field effect. For a group of 8 women, the 50% value for perception for hand hair was 17.5 kV/m as opposed to 6.7 kV/m for a group of 60 men tested during the same day.
Low humidity and low temperature caused lower sensitivity, although the influence of individual parameters is not clear. Moisture on hair, created by humid weather or perspiration, increases the sensitivity.
The frequency of the electric field has an effect on the sensation.
Median values of threshold of perception of hair sensations of people as a function of the frequency of the electric field
Figure 3 – Median values of threshold of perception of hair sensations of people as a function of the frequency of the electric field. For “tingling” the 25th percentile also is given.
Results of Project UHV tests performed with different frequencies are shown in Figure 3.
The data indicate a greater sensitivity at lower frequencies. The difference between the effects of 50-Hz and 60-Hz fields is very small and insignificant when com-pared with the large dispersion of these data.
Of practical interest for transmission-line design applications, are the AC currents flowing through a person’s body from hand to hand or from hand to feet when touching a large object, which collects currents induced by the ac electric field.
Unfortunately, only few data are available for this case, and most data refer to laboratory tests in which people held the electrodes firmly in their hands.
Experimental results from Mr. Dalziel (professor of electrical engineering and computer sciences at UC Berkeley) are shown in Figure 4 for direct current and in Figure 5 for alternating current.
The data follow a normal distribution with large dispersion (ratio 1 to 4 between 1% and 99% values) with average values for men equal to 5.2 mA for direct current and 1.1 mA for 60-Hz alternating current.
Distribution curve of minimum direct and alternating current
Figure 4 – Distribution curve of minimum direct current perceptible data from tests on 115 men; Figure 5 – Distribution curve of minimum alternating current perceptible. Data from 167 men
The first sensation for direct current is that of heat, whereas the first sensation for alternating current is a stinging sensation. Insufficient data are available for women.
As the steady-state intensity of the current increases, control of the muscles in which the current flows becomes increasingly difficult. Above a certain value of current, it is not possible to re-lease the grip on an object. The current for which this situation first occurs is called the let-go-current.
Figure 6 shows the distribution curve of let-go values for different currents.
Distribution curve of let-go value of direct currents
Figure 6 – Distribution curve of let-go value of direct currents. Data from tests on 28 men.
Figure 7 shows the distribution curve for alternating current at 60 Hz. The minimum let-go values are arbitrarily chosen as those corresponding to a probability of 0.5%.
From Figure 7, such values are 9 mA for men and 6 mA for women. A more conservative figure of 5 mA might be applied to children.
Distribution curve of let-go values for alternating currents
Figure 7 – Distribution curve of let-go values for alternating currents. Data for 28 women and 134 men.
The influence of frequency on let-go current is shown in Figure 8 below. Increasing the value of the current above let-go might pro-duce ventricular fibrillation.
Effect of frequency on let-go current
Figure 8 – Effect of frequency on let-go current. The curves re-fer to different percentages of the population for which the let-go conditions are reached.
Fibrillating current values are shown in Figure 9 as a function of body weight for different species of animals. The parameters influencing ventricular fibrillation are body weight, current magnitude, and shock duration.
Dalziel investigated the relation between current and time and proposed an electrocution equation:
i = k / √t
(i in mA, t in seconds).
For a probability of 0.5%, k=165.
Fibrillating currents versus body weight for six species of animals (calves, dogs, sheep, cats, rabbits, guinea pigs)
Figure 9 – Fibrillating currents versus body weight for six species of animals (calves, dogs, sheep, cats, rabbits, guinea pigs). Continuous curves: all animals considered, Dashed curves: guinea pigs omitted.
A summary of the response of adult men to steady-state ac electric currents is shown in Figure 10. The fewer data available for women indicate levels approximately two-thirds of those for men. Data for children are nonexistent.
Let-go values for children for a probability of 0.5% have been conservatively estimated as equal to 5 mA.
Statistical distribution of responses of adult men to steady-state AC currents through a gripped contact
Figure 10 – Statistical distribution of responses of adult men to steady-state AC currents through a gripped contact
Different curves were obtained for rainy and fair-weather days. During rainy days, the umbrella’s material becomes wet and collects more charging current from the at field. Also during rainy days, finger sensitivity is higher because of higher humidity.
Curve 5 corresponds to spark discharges between a small grounded wire and the ankle. The participants were asked to re-main erect, to slowly touch the wire with the ankle, and then to remove the ankle.
Curve 6 corresponds to spark discharges between the tip of the index finger and a grounded rod with a slow approach and release. This last situation was considered as the base case for spark discharges. The discharged capacitance is that of a person to ground, which, for adult men, has an average value of 170 pF.
The median voltage-to-ground was 0.275 kV/(kV/m). From Figure 1 the following median values are obtained:
Median perception threshold:
  • E = 2.7 kV/m
  • Voc = 740V
  • C = 170 pF
Median annoyance level:
  • E = 7 kV/m
  • Voc = 1900V
  • C = 170 pF
The ratio between fields corresponding to 84% and 16% probability is between 2.5 and 4.3.
Results of Project UHV tests performed with different frequencies are shown in Figure 11. The data indicate that people are more sensitive to spark discharges in fields with higher frequency. The difference between the effects of 50-Hz and 60-Hz fields is very small and insignificant when compared with the large dispersion of these data.
Median values of threshold of perception of people exposed to spark discharges as a function of the frequency of the electric field
Figure 11 – Median values of threshold of perception of people exposed to spark discharges as a function of the frequency of the electric field
Stimulation of hair nerves is believed to be the cause of sensations that are above the thresh-old of perception and above the minimum annoyance level.
In practical situations, such stimulation occurs when skin with hair is exposed directly or when currents pass from clothes to body through hair.
These sensations were investigated at Project Code has specified that transmission-line clearances shall be consistent with a maximum induced current of 5 mA, to be calculated for the largest vehicle anticipated under the transmission line and for the final unloaded conductor sag at 49°C.
Abnormal phenomenon under a HV line (VIDEO)
Negative effects of electroMagnetic fields on humans (VIDEO)
Source: 345kV and above transmission line reference book by EPRI
  1. jigme Dorji
    Oct 19, 2022
    Thank you Sir Edvard for sharing such wonderful electrical scientific article about affects of expousure under UHV transmission lines, i have understood very in detail about it. It is very wel determined and measured the human sensitivity from the volunteers to come to such conclusion that the short term affect are noted and such that such long term affect are also to be determined for under various circumtances and condition.
    Thnk you, Sir Edvard.
    I am hoping to have such article post in future from you.
  2. Yasutsugu Ohki
    Feb 01, 2019
    Thank you for nice submission at all times. Japanese regulation require to keep less than 3 kV/m in observing at 1 m above ground level in each case of DC and AC regardless of any frequency.
Leave a Reply to Yasutsugu Ohki