Home / Technical Articles / Theorems and network reductions that every electrical engineer MUST know
Power system analysis
Most practical power system problems are solved by using steady state analytical methods. These methods make the assumption that circuit parameters are linear, bilateral, and constant for constant frequency circuit variables.
When analysing initial values, it is necessary to study the behaviour of a circuit in the transient state. This can be achieved using operational methods.
In some problems, which fortunately are rare, the assumption of linear, bilateral circuit parameters is no longer valid. Such problems are solved using advanced mathematical techniques that are beyond the scope of this article.
Contents:
  1. Circuit Laws (brief descriptions)
  2. Circuit Theorems (brief descriptions)
    1. Superposition Theorem (general network theorem)
    2. Thévenin’s Theorem (active network reduction theorem)
    3. Kennelly’s Star/Delta Theorem (passive network reduction theorem)
  3. Network Reduction
    1. Case a
    2. Case b
    3. Case c
In linear, bilateral circuits, there are three basic network laws. These laws apply, regardless of the state of the circuit, and at any particular instant of time.
These laws are the branch, junction and mesh laws, derived from Ohm and Kirchhoff, and are stated below, using steady state a.c. nomenclature.
1.1 Branch law
The current I in a given branch of impedance Z is proportional to the potential difference V appearing across the branch, that is:
Branch law formulae
1.2 Junction law
The algebraic sum of all currents entering any junction (or node) in a network is zero, that is:
Junction law formulae
1.3 Mesh law
The algebraic sum of all the driving voltages in any closed path (or mesh) in a network is equal to the algebraic sum of all the passive voltages (products of the impedances and the currents) in the component branches, that is:
Mesh law formulae
Alternatively, the total change in potential around a closed loop is zero.
From the above network laws, many theorems have been derived for the rationalization of networks, either to reach a quick, simple, solution to a problem or to represent a complicated circuit by an equivalent.
These theorems are divided into two classes: those concerned with the general properties of networks and those concerned with network reduction.
Of the many theorems that exist, the three most important are given. These are:
  1. Superposition Theorem,
  2. Thévenin’s Theorem and
  3. Kennelly’s Star/Delta Theorem.
2.1 Superposition Theorem (general network theorem)
The resultant current that flows in any branch of a network due to the simultaneous action of several driving voltages is equal to the algebraic sum of the component currents due to each driving voltage acting alone with the remainder short-circuited.
2.2 Thévenin’s Theorem (active network reduction theorem)
Any active network that may be viewed from two terminals can be replaced by single driving voltage acting in series with single impedance.
The driving voltage is the open-circuit voltage between the two terminals and the impedance is the impedance of the network viewed from the terminals with all sources short-circuited.
2.3 Kennelly’s Star/Delta Theorem (passive network reduction theorem)
Any three-terminal network can be replaced by a delta or star impedance equivalent without disturbing the external network. The formulae relating the replacement of a delta network by the equivalent star network is as follows:
Replacement of a delta network by the equivalent star network
and so on.
Star/Delta network reduction
Figure 1 – Star/Delta network reduction
The impedance of a delta network corresponding to and replacing any star network is:
and so on.
The aim of network reduction is to reduce a system to a simple equivalent while retaining the identity of that part of the system to be studied.
For example, consider the system shown in Figure 2.
The network has two sources E’ and E” , a line AOB shunted by an impedance, which may be regarded as the reduction of a further network connected between A and B, and a load connected between O and N.
The object of the reduction is to study the effect of opening a breaker at A or B during normal system operations or of a fault at A or B. Thus the identity of nodes A and B must be retained together with the sources, but the branch ON can be eliminated, simplifying the study.
Proceeding, A, B, N, forms a star branch and can therefore be converted to an equivalent delta.
Typical power system
Figure 2 – Typical power system
Network reduction impedances
(Since ZNO >> ZAOZBO)
The network is now reduced as shown in Figure 3.
Reduction using star/delta transform
Figure 3 – Reduction using star/delta transform
By applying Thévenin’s theorem to the active loops, these can be replaced by a single driving voltage in series with impedance, as shown in Figure 4.
Reduction of active meshes: Thévenin's theorem
Figure 4 – Reduction of active meshes: Thévenin’s theorem
The network shown in Figure 2 is now reduced to that shown in Figure 3.12 with the nodes A and B retaining their identity. Further, the load impedance has been completely eliminated.
The network shown in Figure 5 may now be used to study system disturbances, for example power swings with and without faults.
Reduction of typical power system
Figure 5 – Reduction of typical power system
Most reduction problems follow the same pattern as the example above. The rules to apply in practical network reduction are:
  1. Decide on the nature of the disturbance or disturbances to be studied.
  2. Decide on the information required, for example the branch currents in the network for a fault at a particular location.
  3. Reduce all passive sections of the network not directly involved with the section under examination.
  4. Reduce all active meshes to a simple equivalent, that is, to a simple source in series with a single impedance.
With the widespread availability of computer-based power system simulation software, it is now usual to use such software on a routine basis for network calculations without significant network reduction taking place. However, the network reduction techniques given above are still valid, as there will be occasions where such software is not immediately available and a hand calculation must be carried out.
In certain circuits, for example parallel lines on the same towers, there is mutual coupling between branches. Correct circuit reduction must take account of this coupling.
Three cases are of interest. These are:
  1. Case a: two branches connected together at their nodes
  2. Case b: two branches connected together at one node only
  3. Case c: two branches that remain unconnected
Considering each case in turn:
Case a
Consider the circuit shown in Figure 6(a).
Reduction of two branches with mutual coupling
Figure 6 – Reduction of two branches with mutual coupling
The application of a voltage V between the terminals P and Q gives:
where: Ia and Ib are the currents in branches a and b, respectively and I = Ia + Ib , the total current entering at terminal P and leaving at terminal Q.
Solving for Ia and Ib:
Current Ia
from which
Current Ib
and
Current I
so that the equivalent impedance of the original circuit is (see Figure 6b):
Equivalent impedance of the original circuit
and, if the branch impedances are equal, the usual case, then (see Figure 6c):
Equivalent impedance if the branch impedances are equal
Case b
Consider the circuit in Figure 7(a)
Reduction of mutually-coupled branches with a common terminal
Figure 7 – Reduction of mutually-coupled branches with a common terminal
The assumption is made that an equivalent star network can replace the network shown. From inspection with one terminal isolated in turn and a voltage V impressed across the remaining terminals it can be seen that:
Impedances Za, Zb and Zc
Solving these equations gives (see Figure 7b):
Case c
Consider the four-terminal network given in Figure 8(a), in which the branches 11′ and 22′ are electrically separate except for a mutual link.
The equations defining the network are:
Four-terminal network currents and voltages
where Z12 = Z21 and Y12 = Y21, if the network is assumed to be reciprocal. Further, by solving the above equations it can be shown that:
There are three independent coefficients, namely Z12, Z11, Z22 so the original circuit may be replaced by an equivalent mesh containing four external terminals, each terminal being connected to the other three by branch impedances as shown in Figure 7(b).
Equivalent circuits for four terminal network with mutual coupling
Figure 7 – Equivalent circuits for four terminal network with mutual coupling
In order to evaluate the branches of the equivalent mesh, let all points of entry of the actual circuit be commoned except node 1 of circuit 1, as shown in Figure 7(c). Then all impressed voltages except V1 will be zero and:
Branches formulae
If the same conditions are applied to the equivalent mesh, then:
Branches formulae
These relations follow from the fact that the branch connecting nodes 1 and 1′ carries current I1 and the branches connecting nodes 1 and 2′ and 1′ and 2 carry current I2. This must be true since branches between pairs of commoned nodes can carry no current.
By considering each node in turn with the remainder commoned, the following relationships are found:
Z11', Z22', Z12 formulae
Hence:
Z11', Z22' and Z12 formulae
A similar but equally rigorous equivalent circuit is shown in Figure 7(d). This circuit follows from the reasoning that since the self-impedance of any circuit is independent of all other circuits it need not appear in any of the mutual branches if it is lumped as a radial branch at the terminals.
So putting Z11 and Z22, equal to zero in the last equation, defining the equivalent mesh in Figure 7(b), and inserting radial branches having impedances equal to Z11 and Z22 in terminals 1 and 2, results in Figure 7(d).
Source: Network protection & automation guide by Alstom Grid
  1. Pawan Singh
    May 08, 2019
    Features to be considered in undergrounding overhead Power lines in distribution
