Home / Technical Articles / The basic calculation of transmission line protection
Transmission line protection
The excessive currents accompanying a fault, are the basis of overcurrent protection schemes. For transmission line protection in interconnected systems, it is necessary to provide the desired selectivity such that relay operation results in the least service interruption while isolating the fault.
The basic calculation of transmission line protection (photo credit: acrastyle.co.uk)
This is referred to as relay coordination.
Many methods exist to achieve the desired selectivity. Time/current gradings are involved in three basic methods discussed below for radial or loop circuits where there are several line sections in series.
Three Methods of Relay Grading
  1. Time Grading
  2. Current Grading
  3. Inverse-Time Overcurrent Relaying
1. Time Grading
Time grading ensures that the breaker nearest to the fault opens first, by choosing an appropriate time setting for each of the relays. The time settings increase as the relay gets closer to the source. A simple radial system shown in Figure 1 demonstrates this principle.
Principles of Time Grading
Figure 1 – Principles of Time Grading
A protection unit comprising a definite time-delay overcurrent relay is placed at each of the points 2, 3, 4, and 5. The time-delay of the relay provides the means for selectivity. The relay at circuit breaker 2 is set at the shortest possible time necessary for the breaker to operate (typically 0.25 second).
The relay setting at 3 is chosen here as 0.5 second, that of the relay at 4 at 1 second, and so on. In the event of a fault at F, the relay at 2 will operate and the fault will be isolated before the relays at 3, 4, and 5 have sufficient time to operate.
The shortcoming of the method is that the longest fault-clearing time is associated with the sections closest to the source where the faults are most severe.
Go back to Methods of Relay Grading Methods ↑
2. Current Grading
Fault currents are higher the closer the fault is to the source and this is utilized in the current-grading method. Relays are set to operate at a suitably graded current setting that decreases as the distance from the source is increased.
Figure 2 shows an example of a radial system with current grading. The advantages and disadvantages of current grading are best illustrated by way of examples.
Current Grading for a Radial System
Figure 2 – Current Grading for a Radial System
The inverse-time overcurrent relay method evolved because of the limitations imposed by the use of either current or time alone. With this method, the time of operation is inversely proportional to the fault current level, and the actual characteristics are a function of both time and current settings.
Figure 3 shows some typical inverse-time relay characteristics.
Comparison of CO Curve Shapes
Figure 3 – Comparison of CO Curve Shapes
Relay type CO-7 is in common use. Figure 4 shows a radial system with time-graded inverse relays applied at breakers 1, 2, and 3. For faults close to the relaying points, the inverse-time overcurrent method can achieve appreciable reductions in fault-clearing times.
Time-Graded Inverse Relaying Applied to a Radial System
Figure 4 – Time-Graded Inverse Relaying Applied to a Radial System
The operating time of the time-overcurrent relay varies with the current magnitude. There are two settings for this type of relay:
  1. Pickup current is determined by adjusted current coil taps or current tap settings (C.T.S.). The pickup current is the current that causes the relay to operate and close the contacts.
  2. Time dial refers to the reset position of the moving contact, and it varies the time of operation at a given tap setting and current magnitude.
The time characteristics are plotted in terms of time versus multiples of current tap (pickup) settings, for a given time dial position.
There are five different curve shapes referred to by the manufacturer:
  • CO-11 Extreme inverse
  • CO-9 Very inverse
  • CO-8 Inverse
  • CO-7 Moderately inverse
  • CO-6 Definite minimum
These shapes are given in Figure 3 above.
Example with 11 kV radial system
Consider the 11 kV radial system shown in Figure 5. Assume that all loads have the same power factor. Determine relay settings to protect the system assuming relay type CO-7 (with characteristics shown in Figure 6) is used:
An Example Radial System
Figure 5 – An Example Radial System
CO-7 Time-Delay Overcurrent Relay Characteristics
Figure 6 – CO-7 Time-Delay Overcurrent Relay Characteristics
Solution
The load currents are calculated as follows:
Load currents
The normal currents through the sections are calculated as
Normal currents
With the current transformer ratios given, the normal relay currents are:
Normal relay currents
We can now obtain the current tap settings (C.T.S.) or pickup current in such a manner that the relay does not trip under normal currents. For this type of relay, the current tap settings available are 4, 5, 6, 7, 8, 10, and 12 amperes.
For position 1, the normal current in the relay is 5.25 A. We thus choose:
(C.T.S.)1 = 6 A
For position 2, the normal relay current is 8.53 A, and we choose:
(C.T.S.)2 = 10 A
Similarly for position 3,
(C.T.S.)3 = 10 A
Observe that we have chosen the nearest setting higher than the normal current.
The next task is to select the intentional delay indicated by the time dial setting (T.D.S.). We utilize the short circuit currents calculated to coordinate the relays. The current in the relay at 1 on a short circuit at 1 is:
Expressed as a multiple of the pickup or C.T.S. value, we have:
We choose the lowest T.D.S. for this relay for fastest action. Thus:
By reference to the relay characteristic, we get the operating time for relay 1 for a fault at 1 as:
Operating time for relay 1 for a fault at 1
To set the relay at 2 responding to a fault at 1, we allow 0.1 second for breaker operation and an error margin of 0.3 second in addition to T11 . Thus,
The short circuit for a fault at 1 as a multiple of the C.T.S. at 2 is:
From the characteristics for 0.55-second operating time and 6.25 ratio, we get:
The final steps involve setting the relay at 3. For a fault at bus 2, the short circuit current is 3000 A, for which relay 2 responds in a time T22 obtained as follows:
For a fault at bus 2, the short-circuit current is 3000 A
For the (T.D.S.)= 2, we get from the relay’s characteristic,
For the (T.D.S.)2= 2, we get from the relay’s characteristic
Thus allowing the same margin for relay 3 to respond to a fault at 2, as for relay 2 responding to a fault at 1, we have:
Allowing the same margin for relay 3
The current in the relay expressed as a multiple of pickup is:
Thus for T3= 0.90, and the above ratio, we get from the relay’s characteristic,
Setting the relay at 3
We note here that our calculations did not account for load starting currents that can be as high as five to seven times rated values. In practice, this should be accounted for.
Reference // Electrical Energy Systems by Mohamed E. El-Hawary (Purchase hardcopy from Amazon)
6 Comments
  1. Renjini G S
    Oct 11, 2023
    Dear sir/ Mam,
    Thank you very much for posting such an technical material about Relay coordination. I would like to know about the TDS in detail manner. Is it possible to assume same TDS for all the Relay breakers from Upstream to down of the power flow. In the above case three different TDS values are set for the three different load cases.
  2. raven villanueva
    Oct 15, 2020
    why you didnt use 3200amp in short circuit current 3 in line 3 for determining T.D.S 3? please I want to be clarified thank you so much
  3. EMMANUEL A. TORIBIO
    Jan 14, 2020
    THANK YOU FOR POSTING SUCH EDUCATIONAL DOCUMENT ESSENTIAL TO PROFESSIONAL DEVELOPMENT.
  4. Luis Pablo Murillo R.
    Feb 14, 2017
    Good article, basic but well explained. I suggest to change the article´s name to “Basic calculation for line protection”, without transmission, because it is more general. In fact, time grading protection is not longer used as primary protection for transmission networks. The rules explained in this article is adecuated for radial lines.
  5. Marc Lynch
    Dec 19, 2016
    Hello Mate,
    As an Electrical Engineer in the building services industry I have really enjoyed your articles and regular information pop ups for a few years now.
    One thing I have found myself doing, is copying and pasting the articles into word documents. Is there any way you could set up a downloadable PDF of the articles ? Just a suggestion I feel would enhance the excellent job you’re already doing.
    Best regards,
    Marc
  6. Emmanuel Britto F.
    Dec 16, 2016
    Dear,
    Congratulations for your aproach to the subject.
    I would like to call your attention concerning the 11 kV system.
    At this level very frequent arcing faults occur and in this case, only using overcurrent protection may not be enough as the faulty current may be significantly reduced and the source protection will not detect the fault.
    The use of voltage dependant protections must be then considered so that when arcing occurs and the current be strongly reduced, the faulty condition may be detected by changing the curve level.
    Particular attention must be coped for broken conductors in medium voltage level as even with voltage dependant protections there will be lot of difficulties on detecting this situation. Please refer to specific literature concerning this very delicate matter.
    Kind regards.
Leave a Reply to Luis Pablo Murillo R.
26  −    =  22