Fibre optic systems
In several previous articles I mentioned optical fibre in the context of substation automation, protection signaling, communication between electrical devices, LAN communications, etc. Now I will get into details of fibre optic basics, design, jointing/termination and installation.
Let’s start the discussion following the contents.
  1. The basics of fibre optic systems
  2. What are optical fibres?
  3. Optical cable design
  4. Interconnections, jointing and termination
    1. Fibre splices
    2. Demountable connectors
  5. Installation tips
1. The basics
The fundamental components of a fibre optic system are shown in Figure 1. This system can be used for either analogue or digital transmissions, with a transmitter which converts electrical signals into optical signals.
The optical signals are launched through a joint into an optical fibre, usually incorporated into a cable. Light emitting from the fibre is converted back into its original electrical signal by the receiver.
Basic fibre optic system
Figure 1 – Basic fibre optic system
2. What are Optical fibres?
An optical fibre is a dielectric waveguide for the transmission of light, in the form of a thin filament of very transparent silica glass.
As shown in Figure 2, a typical fibre comprises a core, the cladding, a primary coating and sometimes a secondary coating or buffer. Within this basic construction, fibres are further categorized as multi-mode or single-mode fibres with a step or graded index.
The core is the part of the fibre which transmits light, and it is surrounded by a glass cladding of lower refractive index. In early fibres, the homogeneous core had a constant refractive index across its diameter, and with the refractive index of the cladding also constant (at a lower value) the profile across the whole fibre diameter (as shown in Figure 3(a)) became known as a step index.
In this type of fibre, the light rays can be envisaged as travelling along a zigzag path of straight lines, kept within the core by total reflection at the inner surface of the cladding.
Depending on the angle of the rays to the fibre axis, the path length will differ so that a narrow pulse of light entering the fibre will become broader as it travels. This sets a limit to the rate at which pulses can be transmitted without overlapping and hence a limit to the operating bandwidth.
Basic optical fibre
Figure 2 – Basic optical fibre
To minimize this effect, which is known as mode dispersion, fibres have been developed in which the homogeneous core is replaced by one in which the refractive index varies progressively from a maximum at the centre to a lower value at the interface with the cladding.
Figure 3(b) shows such a graded index fibre, in which the rays no longer follow straight lines. When they approach the outer parts of the core, travelling temporarily faster, they are bent back towards the centre where they travel more slowly.
Thus the more oblique rays travel faster and keep pace with the slower rays travelling nearer the fibre centre. This significantly reduces the pulse broadening effect of step index fibres.
The mode dispersion of step index fibres has also been minimized by the development of single-mode fibres.
Optical fibre categories
Figure 3 – Optical fibre categories
As shown in Figure 3(c), although it is a step index fibre, the core is so small (of the order of 8 µm in diameter) that only one mode can propagate.
Fibre manufacture involves drawing down a preform into a long thin filament. The preform comprises both core and cladding, and for graded index fibres, the core
contains many layers with dopants being used to achieve the varying refractive index.
Although the virgin fibre has a tensile strength comparable to that of steel, its strength is determined by its surface quality.
Microcracks develop on the surface of a virgin fibre in the atmosphere, and the lightest touch or scratch makes the fibre impractically fragile. Thus it must be protected, in line with the glass drawing before it touches any solid object, such as pulleys or drums, by a protective coating of resin, acetate or plastic material, known as the primary coating.
Typically the primary coating has a thickness of about 60 µm, and in some cases a further layer of material called the buffer is added to increase the mechanical protection.
Another type of optical fibre has a plastic construction, with either step or graded index cores. Although larger in size (up to 1.0 mm cladding diameter) and with higher transmission losses than glass fibres, plastic optical fibres have economic and handling advantages for short distance, low data rate communication systems.
Fiber cable structure
The basic aim of a transmission cable is to protect the transmission medium from its environment and the rigours of installation. Conventional cables with metallic conductors are designed to function effectively in a wide range of environments.
However, optical fibres differ significantly from copper wires to an extent that has a considerable bearing on cable designs and manufacturing techniques.
The transmission characteristics and lifetime of fibres are adversely affected by quite low levels of elongation, and lateral compressions can produce small kinks or sharp bends which create an increase in attenuation loss known as microbending loss.
This means that cables must protect the fibre from strain during installation and service, and they must cater for longitudinal compression that occurs, for example with a change in cable temperature.
Fibre life in service is influenced by the presence of moisture as well as stress. The minute cracks which cover the surface of all fibres can grow if the fibre is stressed in the presence of water, so that the fibre could break after a number of years in service.
Cables must be able to provide a long service life in such environments as tightly packed ducts which are filled with water.
The initial application of optical cables was the trunk routes of large telecommunications networks, where cables were directly buried or laid in ducts in very long lengths, and successful cable designs evolved to take into account the constraints referred to earlier.
The advantages of fibre optics soon led to interest in other applications, such as computer and data systems, premises cabling, military systems and industrial control. This meant that cable designs had to cater for tortuous routes of installation in buildings, the flexibility of patch cords and the arduous environments of military and industrial applications.
Further opportunities for optical cables are presented by installations in existing rights-of-way, such as sewers, gas pipes and water lines without the need for costly civil engineering works.
Nevertheless, many of the conventional approaches to cable design can be used for optical cables, with modification to take into account the optical and mechanical characteristics of fibres and their fracture mechanics.
Optical cable elements
Figure 4 – Optical cable elements
Cables generally comprise several elements or individual transmission components, such as copper pairs, or one or more optical fibres. The different types of element used in optical cables are shown in Figure 4 above.
The primary-coated fibre can be protected by a buffer of one or more layers of plastic material as shown in Figure 4(a).
Typically for a two-layer buffer, the inner layer is of a soft material acting as a cushion with a hard outer layer for mechanical protection, the overall diameter being around 850 µm. In other cases, the buffer can be applied with a sliding fit to allow easy stripping over long lengths.
In ruggedized fibres further protection for a buffered fibre is provided by surrounding it with a layer of non-metallic synthetic yarns and an overall plastic sheath. This type of arrangement is shown in Figure 4(b).
When one or more fibres are run loosely inside a plastic tube, as shown in Figure 4(c), they can move freely and will automatically adjust to a position of minimum bending strain to prevent undue stress being applied when the cable is bent. If the fibre is slightly longer than the tube, a strain margin is achieved when the cable is stretched, say during installation, and for underground and duct cables the tube can be filled with a gel to prevent ingress of moisture.
Correct choice of material and manufacturing technique can ensure that the tube has a coefficient of thermal expansion similar to that of the fibre, so that microbending losses are minimized with temperature excursions.
Optical fibres can be assembled into a linear array as a ribbon, as shown in Figure 4(d). Up to 12 fibres may be bonded together in this way or further encapsulated if added protection is required.
In order to prevent undue cable elongation which could stress the fibres, optical cables generally incorporate a strength member. This may be a central steel wire or strand, or non-metallic fibreglass rods or synthetic yarns.
The strength member should be strong, light and usually flexible, although in some cases a stiff strength member can be used to prevent cable buckling which would induce microbending losses in the fibres.
Examples of optical cables
Figure 5 – Examples of optical cables
Strength members are shown in the cable layouts in Figure 5(b) and (c). The strength member can be incorporated in a structural member which is used as a foundation for accommodating the cable elements.
An example is shown in Figure 5(c), where a plastic section with slots is extruded over the strength member with ribbons inserted into the slots to provide high fibre count cables.
A moisture barrier can be provided either by a continuous metal sheath or by a metallic tape with a longitudinal overlap, bonded to the sheath. Moisture barriers can be of aluminium, copper or steel and they may be flat or corrugated. In addition, other cable interstices may be filled with gel or water-swellable filaments to prevent the longitudinal ingress of moisture.
Where protection from external damage is required, or where additional tensile strength is necessary, armouring can be provided. This may be metallic or non-metallic. For outdoor cables, an overall sheath of polyethylene is applied. For indoor cables the sheath is often of low-smoke zero-halogen materials for added safety in the event of fire.
Although the same basic principles of cable construction are used, the wide range of applications result in a variety of cable designs, from simplex indoor patch cords to cables containing several thousand fibres for arduous environments, to suboceanic cables.
Figure 5 shows just a few examples.
The satisfactory operation of a fibre optic system requires effective jointing and termination of the transmission medium in the form of fibre-to-fibre splices and fibre connections to repeaters and end equipment.
This is particularly important because with very low loss fibres the attenuation due to interconnections can be greater than that due to a considerable length of cable.
For all types of interconnection there is an insertion loss, which is caused by Fresnel reflection and by misalignment of the fibres. Fresnel reflection is caused by the changes in refractive index at the fibre–air–fibre interface (Figure 6), but it can be minimized by inserting into the air gap an index-matching fluid with the same refractive index as the core.
Partial transmission and reflection of a pulse travelling from a low to high refractive index medium.
Figure 6 – Partial transmission and reflection of a pulse travelling from a low to high refractive index medium.
Misalignment losses arise from three main sources as shown in Figure 7. Interconnection designs aim to minimize these losses. End-face separation (Figure 7(a)) allows light from the launch fibre to spread so that only a fraction is captured by the receive fibre.
This should therefore be minimized.
Sources of misalignment loss
Figure 7 – Sources of misalignment loss
Normally the fibre cladding is used as the reference surface for aligning fibres, and the fibre geometry is therefore important, even when claddings are perfectly aligned.
Losses due to lateral misalignment (see Figure 7(b)) will therefore depend on the core diameter, non-circularity of the core, cladding diameter, non-circularity of the cladding and the concentricity of the core and cladding in the fibres to be jointed.
Angular misalignment can result in light entering the receive fibre at such an angle that it cannot be accepted.
It follows that very close tolerances are required for the geometry of the joint components and the fibres to be jointed, especially with single-mode fibres with core diameters of 8 µm and cladding diameters of 125 µm.
The main types of interconnections are fibre splices and demountable connectors.
Fibre splices
Fibre splices are permanent joints made between fibres or between fibres and device pigtails. They are made by fusion splicing or mechanical alignment. In fusion splicing, prepared fibres are brought together, aligned and welded by local heating combined with axial pressure.
Sophisticated portable equipment is used for fusion splicing in the field. This accurately aligns the fibres by local light injection and it carries out the electric arc welding process automatically.
Nevertheless, a level of skill is required in the preparation of the fibres, stripping the buffers and coatings and cleaving the fibres to achieve a proper end face.
There are a number of mechanical techniques for splicing fibres which involve fibre alignment by close tolerance tubes, ferrules and v-grooves, and fixing by crimps, glues or resins. Both fusion and mechanical splicing techniques have been developed to allow simultaneous splicing of fibres which are particularly suitable for fibre ribbons.
For a complete joint, the splices must be incorporated into an enclosure which is suitable for a variety of environments, such as underground chambers or pole tops.
The enclosure must also terminate the cables and organize the fibres and splices, and cassettes are often used where several hundred splices are to be accommodated.
Demountable connectors provide system flexibility, particularly at and within the transmission equipment and distribution panels, and they are widely used on patch cords in certain data systems.
As with splices, the connector must minimize Fresnel and misalignment loss, but it must also allow for repeated connection and disconnection, it must protect the fibre end face and it must cater for mechanical stress, such as tension, torsion and bending.
There are many designs but in general the tolerances which are achievable on the dimensions of the various components result in a higher optical loss than in a splice.
Demountable connectors have also been developed for multiple-fibre simultaneous connection, with array designs being particularly suitable for fibre ribbons.
For connector-intensive systems, such as office data systems, use is made of factory-predetermined cables and patch cords to reduce the need for on-site termination.
Optical fibre cables are designed so that normal installation practices and equipment can be used wherever possible.
As they generally have a lower strain limit than metallic cables special care may be needed in certain circumstances and manufacturer’s recommendations regarding tensile loads and bending radius should be followed.
Special care may be required in the following circumstances:
  1. Because of their light weight, optical cables can be installed in greater lengths than metallic cables. For long underground ducts access may be needed at intermediate points for additional winching effort and space should be allowed for larger cable deployment.
  2. Mechanical fuses and controlled winching may be necessary to ensure that the rated tensile load is not exceeded.
  3. Guiding equipment may be necessary to avoid subjecting optical cables to unacceptable bending stresses, particularly when the cable is also under tension.
  4. When installing cables in trenches the footing should be free from stones. These could cause microbending losses.
  5. In buildings, and particularly in risers, cleats and fixings should not be overtightened, or appropriate designs should be used to prevent compression and the resulting microbending losses.
  6. Indoor cable routes should provide turning points if a large number of bends is involved. Routes should be as straight as possible.
  7. Excess lengths for jointing and testing of optical cables are normally greater that those required for metallic cables.
  8. Where non-metallic optical cables are buried, consideration of the subsequent location may be necessary. Marker posts and the incorporation of a location wire may be advisable.
Blown fibre systems have been developed as a means of avoiding fibre overstrain for complex route installation and of allowing easy system upgrading and future proofing.
It results in low initial capital costs and provides for the distribution of subsequent costs. Initially developed by British Telecom, the network infrastructure is created by the most appropriate cabling method, being one or a group of empty plastic tubes.
As and when circuit provision is required, one or more fibres can be blown by compressed air into the tubes. Individual tubes can, by means of connectors, be extended within buildings up to the fibre terminating equipment.
The efficient installation of fibres into the tube network often requires the use of specially-designed fibres and equipment, such as air supply modules, fibre insertion tools and fibre pay-offs.
For installation it is necessary to follow the instructions provided by the supplier, taking into account the requirements for the use of portable electrical equipment and compressed air, and the handling, cutting and disposal of optical fibres.
A novel variation of this system is a data cable used for structural wiring systems.
Reference // Electrical Power Engineer’s Handbook by D.F. Warne (Purchase hardcopy from Amazon)