Home / Technical Articles / Things About MCBs That Every Low Voltage Electrician Should Know
MCB Operation and characteristics
Miniature circuit breaker – MCB is a thermo-magnetic device, meaning that it has two methods of circuit interruption. A thermal mechanism, usually a bi-metallic strip, provides protection against moderate overcurrent.
The heating action of the current causes the bi-metallic strip to curve and break circuit contact. This method is complemented by a solenoid designed to respond to larger currents.
A diagram of an MCB is shown in Figure 1 below.
Figure 1 - Internal view of an MCB
Figure 1 – Internal view of an MCB
It should be apparent that the thermal trip has a slow response time and the solenoid trip has a rapid response time. When combined, these devices provide quite a sophisticated protection characteristic profile.
Table 1 //
BS EN 60898 device thermal characteristics
CurrentDesired Result
 1.13 In Must not trip within 1 h
 1.45 In ≤ 63A Must trip within 1 h
 1.45 x In, > 63A Must trip within 2 h
 2.55 In ≤ 32A Must trip between 1 and 60 s
 2.55 In, > 32A Must trip between 1 and 120 s
The two MCB’s characteristics are described:
  1. Thermal characteristic
  2. Magnetic characteristic
The thermal, bi-metallic characteristic is summarized in Table 1. A further co-ordination of the requirement is that of Regulation 433.1.1 (iii) which is:
I2 ≤ 1.45 × Iz where I2 is the current that causes operation of the device.
By studying Table 1 above, it can be seen that this requirement is built into the product standard for BS EN 60898 devices and is effectively the calibration of the bi-metallic strip.
Go back to Characteristics ↑
The maximum rated current available for MCBs is 125A, and these BS EN 60898 devices are available with different magnetic sensitivities, denoted with a prefix B, C or D accordingly.
The different magnetic characteristics of BS EN 60898 circuit breakers are provided in Appendix 3 of BS 7671: 2008, but to illustrate the differences in the magnetic characteristics, Figure 2 shows a comparison of B, C and D types for devices of the same basic rating. A 32A circuit breaker with type C sensitivity is denoted C32, and it is a requirement of the equipment standard to apply this marking to the device.
The stated B, C or D sensitivities each have a minimum current that causes operation, and this is conventionally taken to be operation within 0.1 second. This is conventionally termed instantaneous operation or instantaneous tripping.
This minimum time convention is due to the mechanics of the circuit breaker, which will always require a certain minimum time, regardless of current for the trip mechanism to open.
Figure 2 - 32A MCB sensitivity characteristics comparison
Figure 2 – 32A MCB sensitivity characteristics comparison
Figure 2 shows that in order to achieve instantaneous tripping or tripping at 0.1 s, a 32A type B breaker requires 160A, a type C breaker 320A and a type D breaker 640A.
Table 2 //
Circuit breaker (BS EN 60898) selection for inrush current applications
TypeManufactured magnetic trip setting
(× In)
Typical applications
B3 to 5General domestic and resistive loads
C5 to 10Small motors (a few kW), small transformers fluorescent lighting and most inductive loads
D10 to 20DOL motors, large star delta motors, low- pressure sodium discharge lighting, larger transformers, welding machine supplies
Below these threshold currents the thermal mechanism is dominant, and has the same characteristic for all three devices. The magnetic characteristics determine the sensitivity type. Equipment connected or likely to be connected to the circuit must be assessed in terms of likely peak or inrush current.
Inrush current is the current that a load draws when the supply is switched on.
Values can range from being insignificant (a few times the normal current), 5 to 10 times normal current for iron core transformers (e.g. conventional ballast fluorescent luminaires) and up to 20 times normal current for much modern electronic equipment, including the power supplies found in user equipment.
While short-lived (often the peak current is a few milliseconds), this can cause circuit breakers to trip, but assessing the likelihood of a circuit breaker tripping is complicated. Table 2 above recommends circuit breaker types for typical inrush current applications.
Separately to inrush current, load peak current also needs to be considered. Peak current in respect of circuit breaker selection is a term used to describe a peak within the normal operation of a cyclic or time varying load.
If you have loads with significant cyclic peaks you need to confirm that the circuit breaker will not trip. This can be confirmed by studying the circuit breaker characteristic curve, but confirmation with the manufacturer may be necessary.
Circuit Breakers – How they Work, What’s Inside
How does a Miniture Circuit Breaker (MCB) work
Reference // Guide to the Wiring Regulations – Darrell Locke IEng MIEE ACIBSE
30 Comments
  1. Sumesh V
    Jul 17, 2023
    Sir,
    It is learned that, the let through energy of a 32A MCB is 1110000A2Sec.
    Let me kindly be informed, how this value is arrived.
  2. Yoong
    May 31, 2023
    Pls review table 1 against IEC 60898.
  3. Ganagalla Polaraju
    Mar 28, 2021
    Can I use above image in my YouTube channel for explanation..
  4. Abdul Seaforth
    Mar 12, 2021
  5. Draoui Abdelghani
    Jun 19, 2018
    Clear and concise explanation , thank you so much :) .
  6. Arslan Tariq
    Dec 31, 2017
    Nice one sir. Thanks for so much info through this portal.
  7. Doug Tucker
    Mar 28, 2017
    Excellent article. Everything you need to know about ‘breakers’ summarised
  8. Joshua
    Jun 08, 2016
    Sir edvard thank you…sir if i may ask what are the common tests done to a building during the turnover or testing and commissioning? thanks and God Bless.
  9. Joshua
    Jun 08, 2016
    Thank you sir edvard for this…God Bless…would just like to ask sir what are the tests conducted on a building during turnover or testing and commissioning exercises? Thanks again sir.
  10. S.Yasitharan
    Oct 21, 2015
    excellent this is very use full to Me Thank a lot ….
  11. Mohammad Omar Thapet
    Oct 08, 2015
    Hello everybody I have 220 VAC /20A circuit breaker can I use it for 12 VDC of 20A load ? Please help me.
  12. Yuva
    Sep 28, 2015
    Good news
  13. Pavel Bulka
    Sep 06, 2015
    Hi, Edvard!
    I hope You are Ok!
    I’m got from You another important informations in my job.
    Thank You!
      Excellent, I’m glad for you!
  14. Tyler
    Aug 25, 2015
    Thank you for your insight and information. Great Information for my customers. Can we share this?
      Sure, that’s the whole point :)
  15. Milivoj *Mil) Zec
    Aug 25, 2015
    Maybe what is missing is the use of MCB in DC. Tripping values are different. Unless I have overlooked it?
    Regards Mil Zec
      Good notice, but I haven’t consider DC MCB at all, it’s about the most common AC MCBs.
  16. mahmoud sayed
    Aug 25, 2015
    thank you edvard hope too much progress for you and your partenrs
  17. piet
    Aug 24, 2015
    very interesting
  18. San
    Aug 24, 2015
    Hi Edvard,
    Then there is overload capability for MCBs ?
    for how many times In and for how long?
      Yes, MCB has circuit protection against both short-circuit currents and overload currents. On this example from main picture, MCB with B curve will trip on 3,5xIn and without any delay, immediately.
  19. Tarek El-Shennawy
    Aug 23, 2015
    Thanks Edvard, I used to teach faculty of engineering students a distribution course, can I use the material supplied in this technical note?
  20. Stephen Peacock
    Aug 22, 2015
    Another very informative and concise reference.
      Thank you Stephen.
      • Bharath
        Aug 22, 2015
        In the MCB image above c60HB means..
          This is the complete meaning of MCB nameplate from above MCB picture:
          C60 – Circuit breaker model number (Schneider Electric // Merlin Gerin)
          B – Magnetic characteristic, type B
          H – Limitation capability of MCB, in this case of 3-pole up to 63A (like on pic) is 15kA
          B32 – Tripping curve, set to 32A
          415V – Operating voltage
          10000 – Rated breaking capacity (in Amps)
          3 – I2t classification