Earthing in electrical network
The main reason for doing earthing in electrical network is for the safety. When all metallic parts in electrical equipment are grounded then if the insulation inside the equipment fails there are no dangerous voltages present in the equipment case.
If the live wire touches the grounded case then the circuit is effectively shorted and fuse will immediately blow. When the fuse is blown then the dangerous voltages are away.
Purpose of Earthing
1. Safety for Human life / Building /Equipment
- To save human life from danger of electrical shock or death by blowing a fuse i.e. To provide an alternative path for the fault current to flow so that it will not endanger the user
- To protect buildings, machinery & appliances under fault conditions.
- To ensure that all exposed conductive parts do not reach a dangerous potential.
- To provide safe path to dissipate lightning and short circuit currents.
- To provide stable platform for operation of sensitive electronic equipment i.e. To maintain the voltage at any part of an electrical system at a known value so as to prevent over current or excessive voltage on the appliances or equipment .
2. Over voltage protection
Lightning, line surges or unintentional contact with higher voltage lines can cause dangerously high voltages to the electrical distribution system. Earthing provides an alternative path around the electrical system to minimize damages in the System.
3. Voltage stabilization
There are many sources of electricity. Every transformer can be considered a separate source. If there were not a common reference point for all these voltage sources it would be extremely difficult to calculate their relationships to each other.
The earth is the most omnipresent conductive surface, and so it was adopted in the very beginnings of electrical distribution systems as a nearly universal standard for all electric systems.
Conventional methods of earthing
1. Plate type Earthing
- Generally for plate type earthing normal Practice is to use
- Cast iron plate of size 600 mm x600 mm x12 mm. OR
- Galvanized iron plate of size 600 mm x600 mm x6 mm. OR
- Copper plate of size 600 mm * 600 mm * 3.15 mm
- Plate burred at the depth of 8 feet in the vertical position and GI strip of size 50 mmx6 mm bolted with the plate is brought up to the ground level.
- These types of earth pit are generally filled with alternate layer of charcoal & salt up to 4 feet from the bottom of the pit.
2. Pipe type Earthing
For Pipe type earthing normal practice is to use GI pipe [C-class] of 75 mm diameter, 10 feet long welded with 75 mm diameter GI flange having 6 numbers of holes for the connection of earth wires and inserted in ground by auger method.
These types of earth pit are generally filled with alternate layer of charcoal & salt or earth reactivation compound.
Method for Construction of Earthing Pit
- Excavation on earth for a normal earth Pit size is 1.5M X 1.5M X 3.0 M.
- Use 500 mm X 500 mm X 10 mm GI Plate or Bigger Size for more Contact of Earth and reduce Earth Resistance.
- Make a mixture of Wood Coal Powder Salt & Sand all in equal part
- Wood Coal Powder use as good conductor of electricity, anti corrosive, rust proves for GI Plate for long life.
- The purpose of coal and salt is to keep wet the soil permanently.
- The salt percolates and coal absorbs water keeping the soil wet.
- Care should always be taken by watering the earth pits in summer so that the pit soil will be wet.
- Coal is made of carbon which is good conductor minimizing the earth resistant.
- Salt use as electrolyte to form conductivity between GI Plate Coal and Earth with humidity.
- Sand has used to form porosity to cycle water & humidity around the mixture.
- Put GI Plate (EARTH PLATE) of size 500 mm X 500 mm X 10 mm in the mid of mixture.
- Use Double GI Strip size 30 mm X 10 mm to connect GI Plate to System Earthling.
- It will be better to use GI Pipe of size 2.5″ diameter with a Flange on the top of GI Pipe to cover GI Strip from EARTH PLATE to Top Flange.
- Cover Top of GI pipe with a T joint to avoid jamming of pipe with dust & mud and also use water time to time through this pipe to bottom of earth plate.
- Maintain less than one Ohm Resistance from EARTH PIT conductor to a distance of 15 Meters around the EARTH PIT with another conductor dip on the Earth at least 500 mm deep.
- Check Voltage between Earth Pit conductors to Neutral of Mains Supply 220V AC 50 Hz it should be less than 2.0 Volts.
Factors affecting on Earth resistivity
1. Soil Resistivity
It is the resistance of soil to the passage of electric current. The earth resistance value (ohmic value) of an earth pit depends on soil resistivity. It is the resistance of the soil to the passage of electric current.
It varies from soil to soil. It depends on the physical composition of the soil, moisture, dissolved salts, grain size and distribution, seasonal variation, current magnitude etc. In depends on the composition of soil, Moisture content, Dissolved salts, grain size and its distribution, seasonal variation, current magnitude.
2. Soil Condition
Different soil conditions give different soil resistivity. Most of the soils are very poor conductors of electricity when they are completely dry. Soil resistivity is measured in ohm-meters or ohm-cm.
Soil plays a significant role in determining the performance of electrode. Soil with low resistivity is highly corrosive. If soil is dry then soil resistivity value will be very high. If soil resistivity is high, earth resistance of electrode will also be high.
3. Moisture
Moisture has a great influence on resistivity value of soil. The resistivity of a soil can be determined by the quantity of water held by the soil and resistivity of the water itself. Conduction of electricity in soil is through water.
Therefore, it is essential to pour water in and around the earth pit to maintain moisture in dry weather conditions. Moisture significantly influences soil resistivity.
4. Dissolved salts
Pure water is poor conductor of electricity. Resistivity of soil depends on resistivity of water which in turn depends on the amount and nature of salts dissolved in it.
Small quantity of salts in water reduces soil resistivity by 80%. Common salt is most effective in improving conductivity of soil. But it corrodes metal and hence discouraged.
5. Climate Condition
Increase or decrease of moisture content determines the increase or decrease of soil resistivity. Thus in dry whether resistivity will be very high and in monsoon months the resistivity will be low.
6. Physical Composition
Different soil composition gives different average resistivity. Based on the type of soil, the resistivity of clay soil may be in the range of 4 – 150 ohm-meter, whereas for rocky or gravel soils, the same may be well above 1000 ohm-meter.
7. Location of Earth Pit
The location also contributes to resistivity to a great extent. In a sloping landscape, or in a land with made up of soil, or areas which are hilly, rocky or sandy, water runs off and in dry weather conditions water table goes down very fast. In such situation back fill compound will not be able to attract moisture, as the soil around the pit would be dry.
Though back fill compound retains moisture under normal conditions, it gives off moisture during dry weather to the dry soil around the electrode, and in the process loses moisture over a period of time. Therefore, choose a site that is naturally not well drained.
8. Effect of grain size and its distribution
Grain size, its distribution and closeness of packing are also contributory factors, since they control the manner in which the moisture is held in the soil.
Effect of seasonal variation on soil resistivity: Increase or decrease of moisture content in soil determines decrease or increase of soil resistivity. Thus in dry weather resistivity will be very high and during rainy season the resistivity will be low.
9. Effect of current magnitude
Soil resistivity in the vicinity of ground electrode may be affected by current flowing from the electrode into the surrounding soil. The thermal characteristics and the moisture content of the soil will determine if a current of a given magnitude and duration will cause significant drying and thus increase the effect of soil resistivity.
10. Area Available
Single electrode rod or strip or plate will not achieve the desired resistance alone.
If a number of electrodes could be installed and interconnected the desired resistance could be achieved. The distance between the electrodes must be equal to the driven depth to avoid overlapping of area of influence. Each electrode, therefore, must be outside the resistance area of the other.
11. Obstructions
The soil may look good on the surface, but there may be obstructions below a few feet like virgin rock. In that event resistivity will be affected. Obstructions like concrete structure near about the pits will affect resistivity.
If the earth pits are close by, the resistance value will be high.
12. Current Magnitude
A current of significant magnitude and duration will cause significant drying condition in soil and thus increase the soil resistivity.
Measurement of Earth Resistance by use of Earth Tester
For measuring soil resistivity Earth Tester is used. It is also called the “MEGGER”.
- It has a voltage source, a meter to measure Resistance in ohms, switches to change instrument range, Wires to connect terminal to Earth Electrode and Spikes.
- It is measured by using Four Terminal Earth Tester Instrument. The terminals are connected by wires as in illustration.
- P=Potential Spike and C=Current Spike. The distance between the spikes may be 1M, 2M, 5M, 10M, 35M, and 50M.
- All spikes are equidistant and in straight line to maintain electrical continuity. Take measurement in different directions.
- Soil resistivity =2πLR.
- R= Value of Earth resistance in ohm.
- Distance between the spikes in cm.
- π = 3.14
- P = Earth resistivity ohm-cm.
- Earth resistance value is directly proportional to Soil resistivity value
Measurement of Earth Resistance (Three point method)
In this method earth tester terminal C1 and P1 are shorted to each other and connected to the earth electrode (pipe) under test. Terminals P2 and C2 are connected to the two separate spikes driven in earth. These two spikes are kept in same line at the distance of 25 meters and 50 meters due to which there will not be mutual interference in the field of individual spikes.
Normally, the length of wires should be 10 and 15 meters or in proportion of 62% of ‘D’.
Suppose, the distance of Current Spike from Earth Electrode D = 60 ft, Then, distance of Potential Spike would be 62 % of D = 0.62D i.e. 0.62 x 60 ft = 37 ft.
Four Point Method
In this method 4 spikes are driven in earth in same line at the equal distance. Outer two spikes are connected to C1 & C2 terminals of earth tester. Similarly inner two spikes are connected to P1 & P2 terminals. Now if we rotate generator handle with specific speed, we get earth resistance value of that place.
In this method error due to polarization effect is eliminated and earth tester can be operated directly on A.C.
GI Earthing Vs Copper Earthing
- As per IS 3043, the resistance of Plate electrode to earth (R) = (r/A) X under root(P/A).
- Where r = Resistivity of Soil Ohm-meter.
- A=Area of Earthing Plate m3.
- The resistance of Pipe electrode to earth (R) = (100r/2πL) X loge (4L/d).
- Where L= Length of Pipe/Rod in cm
- d=Diameter of Pipe/Rod in cm.
- The resistivity of the soil and the physical dimensions of the electrode play important role of resistance of Rod with earth.
- The material resistivity is not considered important role in earth resistivity.
- Any material of given dimensions would offer the same resistance to earth. Except the sizing and number of the earthing conductor or the protective conductor.
Pipe Earthing Vs Plate Earthing
- Suppose Copper Plate having of size 1.2m x 1.2m x 3.15mm thick. soil resistivity of 100 ohm-m,
- The resistance of Plate electrode to earth (R)=( r/A)X under root(π/A) = (100/2.88)X(3.14/2.88)=36.27 ohm
- Now, consider a GI Pipe Electrode of 50 mm Diameter and 3 m Long. soil resistivity of 100 Ohm-m,
- The resistance of Pipe electrode to earth (R) = (100r/2πL) X loge (4L/d) = (100X100/2X3.14X300) X loge (4X300/5) =29.09 Ohm.
- From the above calculation the GI Pipe electrode offers a much lesser resistance than even a copper plate electrode.
- As per IS 3043 Pipe, rod or strip has a much lower resistance than a plate of equal surface area.
Length of Pipe Electrode and Earthing Pit
The resistance to earth of a pipe or plate electrode reduces rapidly within the first few feet from ground (mostly 2 to 3 meter) but after that soil resistivity is mostly uniform.
After about 4 meter depth, there is no appreciable change in resistance to earth of the electrode. Except a number of rods in parallel are to be preferred to a single long rod.
Amount of Salt and Charcoal (more than 8Kg)
To reduce soil resistivity, it is necessary to dissolve in the moisture particle in the Soil. Some substance like Salt/Charcoal is highly conductive in water solution but the additive substance would reduce the resistivity of the soil, only when it is dissolved in the moisture in the soil after that additional quantity does not serve the Purpose.
5% moisture in salt reduces earth resistivity rapidly and further increase in salt content will give a very little decrease in soil resistivity.
The salt content is expressed in percent by weight of the moisture content in the soil. Considering 1M3 of Soil, the moisture content at 10 percent will be about 144 kg. (10 percent of 1440 kg). The salt content shall be 5% of this (i.e.) 5% of 144kg, that is, about 7.2kg.
Amount of Water Purring
Moisture content is one of the controlling factors of earth resistivity. Above 20 % of moisture content, the resistivity is very little affected. But below 20% the resistivity increases rapidly with the decrease in moisture content.
Length Vs Diameter of Earth Electrode
Apart from considerations of mechanical strength, there is little advantage to be gained from increasing the earth electrode diameter with the object in mind of increasing surface area in contact with the soil.
The usual practice is to select a diameter of earth electrode, which will have enough strength to enable it to be driven into the particular soil conditions without bending or splitting. Large diameter electrode may be more difficult to drive than smaller diameter electrode.
The depth to which an earth electrode is driven has much more influence on its electrical resistance characteristics than has its diameter.
Maximum allowable Earth resistance
- Major power station = 0.5 Ohm
- Major Sub-stations = 1.0 Ohm
- Minor Sub-station = 2 Ohm
- Neutral Bushing = 2 Ohm
- Service connection = 4 Ohm
- Medium Voltage Network = 2 Ohm
- L.T.Lightening Arrestor = 4 Ohm
- L.T.Pole = 5 Ohm
- H.T.Pole = 10 Ohm
- Tower = 20-30 Ohm
Treatments to for minimizing Earth resistance
- Remove Oxidation on joints and joints should be tightened.
- Poured sufficient water in earth electrode.
- Used bigger size of Earth Electrode.
- Electrodes should be connected in parallel.
- Earth pit of more depth & width- breadth should be made.
Originally published at Electrical Notes and Articles
hello sir , really good explanation. i have some questions hope to find answers
how the overall earth resistance of site is measured or commissioned, all methods talk about one earth pit measurement.
how the neutral of the transformer is solidly earthed ? the earthing pit resistance equal zero or any resistance
suppose ground water is leaking through earth pit as a result of poor water proofing works inside a basement parking area, What will be the possible impacts, Can anyone explain??
Why Lightening arrestor earth values (4ohm) are more than earth pit values. Lightening follows minimum resistance path Then it cold other minimum resistance path.
Most of the contents are plagiarised from my 2006 article titled “Earthing – myths & facts” that I have published in two of the leading industry journals in India.
It is a shame on the author of this post that even the ‘willful’ mistake that I had done in the article is copied as it is, without any correction. That much for the professionalism of the author.
If the author contests this I am ready to produce my original publication, alongwith publication date.
I have noticed this practice in other postings by same author, and not giving credit to the sources.
Funny thing is you will find “copyrights” in Parmar’s blog.
Hello
Please looking for using electric fl
ash making high heating 3000 centigrade in milliseconds
The distance between cathode and anodes 20 centimeter.
Would you make this
Dear Mr. Siva Kumar
I think you are from L&T STC, i have worked in L&T & quit recently, the irony is i found you on google & EEP, so your IP material is of no use if it is not distributed.
Inside L&T you did not bother to circulate it among your colleagues of EAIC.
Mr. Parmar run his blog for educating people, might be a copy paste but much better then storing knowledge to himself.
I stand by him. & you need to improve.
Ashish Pande
Founder
Jyoti Engineering Infrastructure
I have hill side ban-glow .i use 150 kva voltage stabilizer but i have so much power fluctuation that cause my electronic goos have PCB damage . my neutral + earthing voltage is 7/8 volt its so haigh .
so pls suggest me solution
manoj mhatre
we need formula for number of AC earting for 300kwp solar system
so it is advisable to take earth testing before installing any equipment in an existing site?
Hello. Sir, Is it possible to find the resistance of neutral earth electrode of a 3 phase Distribution transformer on load by ampere clamp meter and also with Earth testing meter kindly tell me the method and calculations
For earthing another material is Bentonite clay with Black cotton soil. Anyone suggest for ratio for Bentonite clay and Black cotton soil for 33 kV substation earthing.
Dear Sir,
can we check Earth pit Resistance value in rainy season?
tell me also that it will increase or decrease.
Sir, how the value of earth resistance varies with the various voltage levels?
Dear Sir,
My question is regarding transmission line.
If jumpering work of 800kV HVDC tower is under progress, Line is dead. How shall we protect those workmen in monsoon seasons. Where we shall put the discharge rods if most of the Jumpers are installed??
Thanks for sharing this information, Great Work!
how can you got that 2.88 for A value..
kindly tell me sir
Erll explained.