Home / Technical Articles / Transformer no-load loss and excitation-current measurements
Purpose of no-load loss measurements
A transformer dissipates a constant no-load loss as long as it is energized at constant voltage, 24 h a day, for all conditions of loading. This power loss represents a cost to the user during the lifetime of the transformer.
Transformer no-load loss and excitation-current measurements (photo source: ardantrafo.com)
Maximum values of the no-load loss of transformers are specified and often guaranteed by the manufacturer. No-load-loss measurements are made to verify that the no-load loss does not exceed the specified or guaranteed value.
Average-voltage voltmeter method
Transformer no-load loss, often called core loss or iron loss, is the power loss in a transformer excited at rated voltage and frequency but not supplying load.
The no-load loss comprises three components:
  1. Core loss in the core material
  2. Dielectric loss in the insulation system
  3. I2R loss due to excitation current in the energized winding
The no-load loss of a transformer is primarily caused by losses in the core steel. The remaining two sources are sometimes ignored. As a result, the terms no-load loss, core loss, and iron loss are often used interchangeably. Core loss and iron loss, strictly speaking, refer only to the power loss that appears within the core material.
The following discussion on no-load loss, or core loss, will explain why the average-voltage voltmeter method, to be described later, is recommended.
The magnitude of no-load loss is a function of the magnitude, frequency, and waveform of the impressed voltage. These variables affect the magnitude and shape of the core magnetic flux waveform and hence affect the value of the core loss.
It has been verified through measurements on power and distribution transformers that core loss also depends, to some extent, upon the temperature of the core.
According to the IEEE, ‘Standard Test Code for Liquid-Immersed Distribution, Power, and Regulating Transformers and Guide for Short-Circuit Testing of Distribution and Power Transformers’, the approximate rate of change of no-load loss with core temperature is 0.00065p.u. core loss increase for each °C reduction in core temperature.
The two main components of the core loss are hysteresis loss and eddy-current loss.
The change in eddy-current loss, due to a change in the resistivity of the core steel as temperature changes, appears to be one factor that contributes to the observed core-loss temperature effect. The hysteresis loss magnitude is a function of the peak flux density in the core-flux waveform.
When the impressed voltage waveform is distorted (not a pure sine wave), the resulting peak flux density in the flux waveform depends on the average absolute value of the impressed voltage wave.
Eddy-current loss is a function of the frequency of the power source and the thickness of the core-steel laminations. Eddy loss is strongly influenced by harmonics in the impressed voltage.
The above mentioned IEEE transformer test code recommends the average-voltage voltmeter method, to be described below, for measuring no-load loss.
Excitation current is the current flowing into the high voltage winding with the low voltage side open. This current should be proportional to the No-load acceptance test but with the difference resultant from the use of test voltages different from nominal values.
It shouldn’t exist excessive deflection from values measured between phases and its normal a slight difference (geometric) between extreme and central windings. It will exist great changes when appear heat points, degradation in the magnetic package, loose core or detached magnetic shunt.
How no-load loss is measured
The measurement of no-load loss, according to the average-voltage voltmeter method, is illustrated in Figure 1. Voltage and current transformers are required to scale the inputs for voltmeters, ammeters, and wattmeters.
Three-phase no-load-loss measurements are carried out the same way, except that three sets of instruments and instrument transformers are utilized.
Test circuit for no-load-loss measurement
Figure 1 – Test circuit for no-load-loss measurement
The test involves raising voltage on one winding, usually the low-voltage winding, to its rated voltage while the other windings are in open circuit. Two voltmeters connected in parallel are employed.
The voltmeter labeled Va in Figure 1 represents an average-responding, rms-calibrated voltmeter. The voltmeter labeled Vr represents a true rms-responding voltmeter.
Harmonics in the impressed voltage will cause the rms value of the waveform to be different from the average-absolute (rms-scaled) value, and the two voltmeter readings will differ. When the voltage reading, as measured by the average-responding voltmeter, reaches a value corresponding to the rated voltage of the excited winding, readings are taken of the rms current, the rms voltage, and the no-load power.
The ratio of the measured rms current to the rated load current of the excited winding, expressed in percent, is commonly referred to as the percent excitation current. The measured no-load loss is corrected to a sine-wave basis by a formula given in the mentioned IEEE test code, using the readings of the two voltmeters.
The correction is shown below. The corrected value is reported as the no-load loss of the transformer.
Corrected (reported) value of no-load loss
where:
  • Pc is the corrected (reported) value of no-load loss
  • Pm is the measured value of no-load loss
  • Va is the reading of the average-responding, rms-calibrated voltmeter
  • Vr is the reading of the true-rms-responding voltmeter
  • P1 and P2 are the per-unit hysteresis and per-unit eddy-current losses, respectively
According to the mentioned IEEE test code, if the actual values of P1 and P2 are not available, it is suggested that the two loss components be assumed equal in value, assigning each a value of 0.5 p.u..
Sources:
  1. The Electric Power Engineering Handbook by Leonard L. Grigsby (Purchase hardcover from Amazon)
  2. Power transformer maintenance – Field Testing by Andrés Tabernero García
7 Comments
  1. Rabi'u' Abdullahi
    Jun 04, 2023
    I am a student of elect elect in one of Nigeria politechnics, my urge to learn more vivid technics in power generations, transmission, distribution, including transformer test and general earh testing.
    Please how do I test earth resistance using multi tester
  2. David
    May 14, 2021
    What would be the power factor behavior under this test?
  3. Larry Butler
    Apr 20, 2021
    Our new L2 EV charging station from Electrify America sits idle and energized 22 hours per day on it’s underground fed 1500 KVA utility transformer. No switchgear is provided to shut it down for the very long periods of no load on its charging power supplies other than 50 watts of green leds to advertise its empty presence. This is NOT efficient at sll. Tesla’s nearby underpowered 750 KVA, 8 stall Supercharger is also hard wired to waste as much coal-fired power as possible. Why so much waste? A small utility transformer, say 5 KVA to run the sinage and electronics that could connect the monsters when demand happens then shuts them down during no load hours to days would be lots more green and profitable. Constant core loss doesn’t make the meter downstream spin for revenue. How stupid.
  4. ACKIM MBEWE
    Jan 06, 2020
    on a 13.8KV/330KV, 180 MVA transformer,what would be the recommended test voltage on the LV side for the No load test to meaningfully achieve the no load loss.
    Available test voltage being 400V
    • abb
      Jan 20, 2020
      You need to maintain the Volt/turn of transformer same.
  5. willy
    Mar 28, 2019
    thanks for this information
  6. Mario Meneses
    Mar 27, 2019
    Excelent information, we thanks that you make this very usefull technical articles
Leave a Reply to ACKIM MBEWE
fifteen  −  thirteen  =
