Selecting and rating MV switchgear

It’s not unusual to see that engineers mix terms of primary ratings. If they are not understood well, yes, it’s possible to mix some of them. But it’s essential to differentiate them. This technical article will try to shed some light on the fundamental primary rated values involved in correct selecting and rating the medium voltage switchgear assembly and its main components.

Primary rated values for medium voltage switchgear
Primary rated values for medium voltage switchgear (on photo: Medium voltage switchgear, type NXAIR by SIemens; credit: Maximilian Huelsing via Linkedin)

Just to mention that the process of designing secondary systems with devices for protection, control, measurement, and counting purposes is not covered here.

Table of contents:

  1. Rated voltage (Ur)
  2. Rated insulation level
  3. Rated short-circuit currents
    1. Rated short-circuit breaking current
    2. Rated short-circuit making current and rated peak current
    3. Rated short-time withstand current
  4. Rated duration of short-circuit (tk)
  5. Rated normal current (Ir)

1. Rated voltage Ur

Definition – The maximum operating voltage of the network (UNmax) – at the upper tolerance limit – and the required insulation level of the equipment determine the rated voltage.

Rating rule: Ur ≥ UNmax and Ur corresponds with the required insulations level (see 2. below)

For switchgear, the next highest standard value above the maximum operating voltage is set as the rated voltage. The value of the maximum operating voltage must cover effects of temporary overvoltages, for example caused by: harmonics, load shedding (generators for emergency supply, customer generation etc.) and capacitive equipment, such as capacitor banks, filters.

If a particular insolation level is pre-determined, the rated voltage must correspond with it.


Recommendations:

Recommendation №1 – The rated voltage of the switchgear may differ from that of voltage transformers, surge arresters, and HRC fuses. This is because these devices are subject to additional rating criteria .

Recommendation №2 – Some switching duties require the switching devices to have an even higher rated voltage, although this is rare. In certain cases, the entire switchgear system must be designed for higher voltages.

Recommendation №3 – Due to the reduced insulating properties tt altitudes of above 1000 m above sea level, a higher rated value may be selected – where applicable (see 2. below).

Recommendation №4 – A higher rated voltage can be set to fulfil the requirements of a higher insulation level in order to cope with special ambient conditions, for example pollution or humidity. (see 2. below).

Go back to Contents Table ↑


2. Rated insulation level

The insulation level comprises the lightning impulse withstand voltage (Up) and the short-duration power-frequency withstand voltage (Ud).

Rating rule: Ur ↔ Ud and Up (see table in IEC 62271-1)

The rated insulation level is assigned to the rated voltage in accordance with table 1a, IEC 62271-1 [1] the applicable standard and is, therefore, set at the same time as the rated voltage. Different allocations must be specified separately.

In medium-voltage systems, the standard insulation levels do not differ with respect to the neutral point earthing

Table 1 – Rated voltages and insulation levels in the medium voltage range

Rated voltage Ur/kV
(r.m.s. value)
Rated short-duration power-frequency withstand voltage
Ud / kV (r.m.s. value)
Rated lightning impulse withstand voltage
Up / kV (peak value)
Line-earth, line-line, across contact gapAcross isolating distanceLine-earth, line-line, across contact gapAcross isolating distance
(1)(2)(3)(4)(5)
3.610 1220, 4023, 46
7.2202340, 6046, 70
12283260, 7570, 85
17.5384575, 9585, 110
24506095, 125110, 145
367080145, 170160, 195
5295110250290

Go back to Contents Table ↑


Comments:

Recommendation №1 – Operators may specify a higher insulation level in accordance with operational requirements. Reasons for this include foreseeable reduction in insulation due to moisture or pollution or high dielectric stresses during standard operation due to connected overhead systems, traction supply systems etc.

Recommendation №2 – At altitudes of at least 1000 m above sea level, the insulation level decreases caused by the
lower air density.

There are alternatives to compensate this decrease:

  • A higher rated voltage is set.
  • Surge arresters are installed to limit possible overvoltages below the actual insulation capability. Based on the voltage withstand value at the relevant altitude (see Figure 1) the required protection level of the arresters is determined.
  • Gas-/solid-insulated switchgear is used with shielded, earthed connections (cable plug connectors, insulated bars), where the HV conductors are nor surrounded by ambient air.

For low-voltage auxiliary and control equipment no precautionary measures need be taken up to 2000 m altitude. Regarding installation sites at higher altitude see IEC 60664-1 [18].

Lightning impulse withstand capability in air, depending on the site altitude
Figure 1 – Lightning impulse withstand capability in air, depending on the site altitude

Example for diagram above: a lightning impulse withstand voltage of Up = 120 kV is required at an altitude of 1800 m. A system with a rated voltage of 36 kV achieves this, while a 24 kV system is not suitable because it can only maintain a lightning impulse withstand voltage of 125 kV up to 1000 m.

Recommendation №3 – In environments with high levels of pollution, longer creepage paths may be required. This can be achieved not only with a higher insulation level, but also with alternative methods:

  • Avoiding unprotected insulation
  • Additional insulation for exposed parts (e.g. heat shrink tube to act as bridging protection)
  • Gas-insulated switchgear with shielded, earthed connections (cable plug connectors, insulated bars)

Note that, in many cases, surge arresters fitted at central points can be used as an alternative to increasing insulation levels.

Go back to Contents Table ↑


3. Rated short-circuit currents

Rated short-circuit currents include:

  1. The peak current Ip and short-circuit making current Ima
  2. The short-time current Ik and short-circuit breaking current Isc

The peak current and short-time current are withstand capability variables (steady state), while the short-circuit making and breaking current indicate the switching capacity. The applicable standard defines a fixed ratio between the impulse and short-time current as a basic design requirement for switching devices and switchgear: Ip/Ik = 2.5 (2.6 at 60 Hz).

The same ratio applies to the dynamic variables Ima/Isc. The values that actually occur in the network, however, have priority.

Membership Upgrade Required

This content is not available in your premium membership plan. Please upgrade your plan in order to access this content. You can choose an annually based Basic, Pro, or Enterprise membership plan. Subscribe and enjoy studying specialized technical articles, online video courses, electrical engineering guides, and papers.

With EEP’s premium membership, you get additional essence that enhances your knowledge and experience in low- medium- and high-voltage engineering fields.

Time Limited! – Save 15% on PRO Membership Plan with coupon CTS15

Upgrade

Already a member? Log in here

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical engineering guides, research studies and much more! It helps you to shape up your technical skills in your everyday life as an electrical engineer.
More Information
Edvard Csanyi - Author at EEP-Electrical Engineering Portal

Edvard Csanyi

Hi, I'm an electrical engineer, programmer and founder of EEP - Electrical Engineering Portal. I worked twelve years at Schneider Electric in the position of technical support for low- and medium-voltage projects and the design of busbar trunking systems.

I'm highly specialized in the design of LV/MV switchgear and low-voltage, high-power busbar trunking (<6300A) in substations, commercial buildings and industry facilities. I'm also a professional in AutoCAD programming.

Profile: Edvard Csanyi

Leave a Comment

Tell us what you're thinking. We care about your opinion! Please keep in mind that comments are moderated and rel="nofollow" is in use. So, please do not use a spammy keyword or a domain as your name, or it will be deleted. Let's have a professional and meaningful conversation instead. Thanks for dropping by!

Learn How to Design Power Systems

Learn to design LV/MV/HV power systems through professional video courses. Lifetime access. Enjoy learning!

EEP Hand-Crafted Video Courses

Check more than a hundred hand-crafted video courses and learn from experienced engineers. Lifetime access included.
Experience matters. Premium membership gives you an opportunity to study specialized technical articles, online video courses, electrical engineering guides, and papers written by experienced electrical engineers.
This whitepaper by OMICRON explores the fundamental shift in substation automation testing from hardware-dependent setups to virtualized, software-defined verification.